Diagnosing a thermostat issue

  • HVAC
  • Thread starter Grinkle
  • Start date
  • Tags
    Condenser
  • #1
Grinkle
Gold Member
772
223
TL;DR Summary
My Gen 1 Nest will no longer turn my condenser on. Any theories on why appreciated.
If you are interested in the thread but don't have any background in the connections I will describe, the below video is a 5 minute description of the control signals and the theory of operation. Its a very informative video.



Some definitions, using what I have learned is the common signal naming convention for thermostat wiring -

"Y" is the control line for cooling, on my system, it controls the condenser, since I don't have a heat pump.

"G" is the control line for the fan, which is in my attic and in the same chasis that contains the A/C control board.

"R" is the high power leg.

"C" is the 'common' aka 'ground' aka 'low power leg' aka 'A/C-'

System working fine for years, then for no reason I can identify perhaps 18 months ago my compressor starts to hiccup on and quickly turn off (once) several times a day (occurrences separated by 10 minutes to a few hours). It does this with the Nest set to "Heat" or "Off" as well as "Cool".

I spend $300 on a couple trips by a tech who can't find a cause.

I turn the power to the condenser off by turning off the 220V breaker that is dedicated to the condenser for a few winter months and do a rain dance to make the problem go away. Ineffectual.

A couple weeks ago I turn the breaker back on and the condenser is still occasionally hiccuping. I don't try to turn the cooling on.

Thinking to debug on my own, I research the connections, find the above video and start poking around. In my poking, I must have changed something in the behavior, probably while I was figuring out how to manually bypass the thermostat. The first time I tried it, the system shut down, I must have tripped a current fault somewhere in the system. Ever since then ...

Nest cannot or will not energize "Y" and the condenser never turns on. I have two Nest thermostats and they both work fine with one of the systems in my home and both have the identical bad behavior in the other system.

I confirmed with a multi-meter that when the Nest says "Cooling", "G" is energized but "Y" is not. The fan is blowing, and the condenser is not on.
Specifically, at the control board in my attic -

R to C gives 24V AC : Power is ok
G to C gives 24V AC : Fan control is energized, fan is on
Y to C gives 0 AC : Condenser is not energized, condenser is not on (unexpected)

I remove the Nest, short R,Y and G and the system (both condenser and fan) turns on normally and cools normally, as I would expect.

IMG-20240402-WA0000.jpeg


I have two cooling systems in my home, they are of different makes, though. One is Trane, one is Lennox. Both are controlled by a Gen 1 Nest.
I swap Nests, and the behavior stays with the system. So both Nest thermostats operate the Trane system normally, and neither Nest turns on the Lennox condenser. So I don't think the Nest unit is faulty.

Thinking the Nest Gen 1 signal drivers might be marginal with the control board on my unit, and as the stuff aged some property of the Y signal changed just enough to put it out of reach, I bought a basic not-smart Honeywell thermostat can tried it out. It works fine. When I turn it to cool, the fan and the condenser come on and the system cools normally.

20240402_131520.jpg


My Nest units are Gen 1. Does anyone suspect a Gen 3 Nest might work differently?

I find it very odd that the Nest does not throw an error when Y is not energized and the Nest is in a mode such that it must be intending to energize Y (the cooling mode). I speculate there may be some current fault detection in the Nest driver that is hardware-only, but I can't think of any way to test for that and I can't find any reference to such a thing on-line.

C is connected to the Nest and the A/C controller, btw. Its an optional connection according to Nest installation instructions, I have it connected and always have.
 

Attachments

  • 20240331_120451.jpg
    20240331_120451.jpg
    33.7 KB · Views: 8
Physics news on Phys.org
  • #2
The 2 leading possibilities:
1. A cable defect (marginal) between the Tstat and the AC
2. An intermittent defect at the main contactor coil.

I've seen both (standing in my backyard at 2:00 AM in my underwear). While not always the case, these kind of intermittent AC issuers are often related to moisture. The cable is subject to atmospheric and (for buried wire) soil moisture. Troubleshooting these is not fun.

-Replace the (or temporarily run a substitute) cable.
-Make sure that nothing (mice, insects...) has set up residence in the control enclosure and there is no excessive dirt/moisture.
 
  • Like
Likes russ_watters
  • #3
@Dullard The cable from the condenser to the blower was replaced by the tech, that didn't change the hiccups. The thermostat cable is short, up the wall into the attic and into the blower, but its quite old and could be marginal.

Along those lines, I wonder if the Nest backplate connector where the Nest plugs in could have a marginal mechanical connection at the Y port. I can swap Nest backplates to check that.

I can easily run a parallel cable, thanks for the suggestion.
 
Last edited:
  • #4
Good Luck. It will make perfect sense (once you figure it out).
 
  • Like
Likes Grinkle
  • #5
A compressor cycling On & Off is frequently caused by low refrigerant level. This is implemented by pressure sensors in the refrigerant plumbing. They exist to protect the compressor from damage due to loss of refrigerant. At least some larger systems have two pressure switches, one each on the low-pressure side and the high-pressure side of the compressor.

A less frequent cause is the over-temperature thermostat in or on the compressor.

Or, of course, a loose wire or a bad relay or, even a bad circuit breaker.

Now for the 'new' failure of things not turning on at all:

0) check that there is power coming in
1) remove thermostat
2) jumper the wires at the thermostat socket to simulate what the thermostat should do
Does the system come on (operate) as expected?
Yes) Either the thermostat(s) failed​
-OR-​
whatever the thermostat drives is faulty​
No) Remove the jumpers and leave the thermostat disconnected​
Connect the jumpers to the appropriate wires in the A/C unit​
Unit works: suspect wiring between unit and thermostat​
Unit does Not work: Well, at least you have localized the problem (sort of) :cry:
Start troubleshooting the things mentioned at the start of this post.​
Cheers,
Tom
 
Last edited:
  • Like
Likes Lnewqban
  • #6
@Tom.G Thanks for the response. I've had a different non-Nest thermostat on the system since I made the OP, and all of the symptoms are gone, the system is working normally. I did the test you describe, and I am here with my own reasoning -

Tom.G said:
2) jumper the wires at the thermostat socket to simulate what the thermostat should do
Does the system come on (operate) as expected?
Yes) Either the thermostat(s) failed-OR-whatever the thermostat drives is faulty

The thermostat drives the Nest back plate, then the thermostat wire, then the system control board in the blower in my attic. The new thermostat uses the same wire, but a different type of back plate than the Nest. I think the wire is ok, because both thermostats use it. I don't have any way to test if the control board is marginal and will work with some thermostat drivers but not others.

I can't test the new thermostat with the old back plate, but I could put the old back plate on the 2nd system in my home and see if it becomes faulty. At this point, though, with all systems working, I think I will let further debug lie and live with having two different kinds of thermostats in my home.
 
  • Informative
Likes Tom.G
  • #7
My Grandfather use to say "If it works, don't F@!%$ with it." This is one of those situations. Grandpa never worked on spacecraft.
 
  • Like
Likes russ_watters

Similar threads

  • Mechanical Engineering
2
Replies
42
Views
3K
  • Thermodynamics
Replies
8
Views
1K
Replies
7
Views
807
Replies
26
Views
2K
  • DIY Projects
Replies
23
Views
4K
  • DIY Projects
Replies
4
Views
2K
  • DIY Projects
Replies
13
Views
3K
Replies
8
Views
850
Replies
47
Views
6K
  • Electrical Engineering
Replies
3
Views
2K
Back
Top