Why Single-wire earth return systems are only used in rural areas?

In summary: SWER systems are more common in rural than urban areas because of the lower cost of hardware. In modern systems, the neutral is required, so SWER is not as common as it once was.
  • #1
Charles123
132
0
Why Single-wire Earth return systems are only used in rural areas? Why not also in urban areas where there is only demand for single phase power?
 
Engineering news on Phys.org
  • #2
Primary reason I would assume would be cost... you only pay for one copper conductor NOT 2 same as they used to do for out of the way rural phone lines

Dave
 
  • #3
Of course that would be the main reason for using it, that`s why the question is why not also in urban areas where there is only demand for single phase power?
 
  • #4
I'll venture a guess, to see whether anyone can shoot this down. :wink:

I seem to recall seeing in rural areas that the single wire feeds a pole-mounted transformer as it passes each isolated farm. The mains return is via an Earth at the power pole, and from the transformer the farmer gets both active and neutral wires. I would expect Earth return to involve appreciable losses, compared with copper return.

So, extending this to suburban areas, almost every power pole would have to incorporate a transformer and a buried Earth return, if we were to avoid twin wires running along the streets.
 
  • #5
This was done for cost - and typically old farm houses used very little power. Really there are 2 conductors missing - a Neutral and a Ground - I do not know if they will allow this type of install today - but they used to then make a secure Earth connection ( Grounding rod ) Really every installation has one, but in this single line type connection the ground rod is actually conducting current.
The Grounding rod actually can have relatively low resistance - back to the pole, ~1 Ohm - but the real issue is that the grounding rod will deteriorate over time - high rate of corrosion due to the current - so this connection needs to be checked and maintained.

In Urban or more densely populated areas the total load is greater and the utility will try to maintain balanced 3 phase loads in their system, but also one transformer will be feeding many customers - typically the transformers in an area will be matched and to do this well they need a neutral. Also - modern feed is 240/120 ( here int he USA) - split phase - this also requires the neutral.
 
  • #6
This Wiki article explains the system.
http://en.wikipedia.org/wiki/Split_phase

You see that the rural residant obtains 2 live wires and a third neutral line that go into his fuse panel. By selection of proper terminals, he/she can have 120 v for lighting and outlets, and 240 v for stoves, dryers just like an an urban residant.
The neutral line could carry a current depending upon how the electrical balance was set up from the fuse panel for circuiitry in the house or other farm building. A ground wire for safety reasons could be set up from the fuse box to the Earth ground.

The main reason for this setup was cost of one wire versus 2 for a long transmission line. And with one resident per transformer, load balance was not that much of a problem. In urban areas, the reverse is true - it is less costly to set up more wires than have a transformer for each dwelling - imagine 10 transformer units on a pole for a 10-unit apartment building.
 
  • #7
Thank you for your answer!
 
  • #8
Single wire Earth return pertains only to the primary (19 kv, etc.) circuit from the substation. Each customer still has a neutral wire (grounded/earthed conductor) in the respective secondary circuit from the pole transformer to the building fuse/breaker panel.

In a SWER system one pole transformer can also server multiple customers.

In rural areas the overall amount of current drawn by the primary circuit (at primary circuit voltages) is usually small enough that the voltage drop across the Earth return is not too great. If the current draw got too large for the Earth conductivity, as would happen in an urban or suburban setting, then the primary voltage and therefore the customers' secondary service voltage would drop noticeably. Because the current draw could vary greatly over the course of a day or even an hour, automatic voltage regulation would be needed.
 
Last edited:

Related to Why Single-wire earth return systems are only used in rural areas?

What is a single-wire earth return system?

A single-wire earth return (SWER) system is an electrical distribution system that uses a single wire to carry both the supply and return currents. The return current is conducted through the earth, rather than a separate wire, making it a cost-effective option for rural areas where there are long distances between customers.

Why are SWER systems only used in rural areas?

SWER systems are only used in rural areas because they are designed for low-voltage, low-power distribution over long distances. In urban areas, there are typically more customers and higher power demands, making a more complex and expensive electrical distribution system necessary.

What are the advantages of using SWER systems in rural areas?

There are several advantages to using SWER systems in rural areas. These include lower installation and maintenance costs, reduced voltage drop over long distances, and the ability to operate with a single-phase supply, which is more suitable for the lower power demands of rural customers.

What are the limitations of SWER systems?

While SWER systems are cost-effective and efficient for rural areas, they do have some limitations. The primary limitation is the power carrying capacity, as SWER systems are not designed for high power demands. They are also more susceptible to interference and voltage fluctuations caused by lightning strikes or ground faults.

Are there any safety concerns with using SWER systems?

Yes, there are some safety concerns with using SWER systems. Since the return current is conducted through the earth, there is a risk of electric shock if the earth connection is damaged or faulty. Additionally, the use of a single wire means that there is no dedicated neutral, which can cause problems with equipment that requires a balanced load.

Similar threads

  • Electrical Engineering
Replies
6
Views
1K
Replies
13
Views
4K
  • Electrical Engineering
3
Replies
83
Views
4K
  • Electrical Engineering
2
Replies
41
Views
14K
  • Electrical Engineering
Replies
3
Views
1K
Replies
7
Views
1K
Replies
1
Views
973
  • Electrical Engineering
Replies
1
Views
1K
  • Electrical Engineering
Replies
1
Views
2K
  • Electrical Engineering
Replies
16
Views
4K
Back
Top