Transformer and Generator in Per Unit System

In summary, the conversation discusses a 3-phase generator connected through a transformer to a transmission line with a series reactance. The base values in the line circuit are given and the task is to find the generator and transformer reactances in per unit for two cases: (i) a 3-phase transformer with a different voltage rating and (ii) a transformer composed of three single-phase units. The equations used to calculate the per unit reactance and the attempts at solving for each case are also mentioned.
  • #1
tommyhakinen
36
0

Homework Statement



A 3-phase generator rated 100 MVA, 13.2 kV, X = 20% is connected through a Δ/Y
transformer to a transmission line whose series reactance is 40 ohms per phase.
Assume that the base values in the line circuit are 200 MVA and 115 kV.
Find the generator and transformer reactances in pu for the following cases:
(i) The transformer is a 3-phase unit rated 100MVA, 13.8Δ/120Y kV, X = 8%.
(ii) The transformer is composed of three single-phase units, each rated 35 MVA,
13.8/69 kV, X = 8%.
 
Physics news on Phys.org
  • #2
Homework Equations X/X_base = X_pu The Attempt at a Solution(i) X_pu = 8/20 = 0.4 puX_base = (200MVA x 115kV)/(100MVA x 13.2kV) = 153.125X = 0.4 x 153.125 = 61.25 ohms(ii) For each single-phase unit,X_pu = 8/20 = 0.4 puX_base = (200MVA x 115kV)/(35MVA x 13.8kV) = 493.75X = 0.4 x 493.75 = 197.5 ohms
 
  • #3




In the per unit system, all quantities are expressed in terms of their corresponding base values. This allows for easier comparison and analysis of different power systems. In this problem, we are given a 3-phase generator rated at 100 MVA and connected through a Δ/Y transformer to a transmission line with a series reactance of 40 ohms per phase. We are also given the base values for the line circuit, which are 200 MVA and 115 kV.

To find the generator and transformer reactances in per unit (pu), we need to first determine the per unit values for voltage and power. We can do this by dividing the actual values by their corresponding base values.

For the generator, the per unit voltage will be 13.2 kV/115 kV = 0.115 pu and the per unit power will be 100 MVA/200 MVA = 0.5 pu.

(i) For the first case, the transformer is a 3-phase unit rated 100MVA, 13.8Δ/120Y kV, X = 8%. Using the same method as above, we can calculate the per unit voltage and power for the transformer. The per unit voltage will be 13.8 kV/120 kV = 0.115 pu and the per unit power will be 100 MVA/200 MVA = 0.5 pu. To find the per unit reactance, we use the formula Xpu = Xactual/Xbase. This gives us a per unit reactance of 0.08 pu for the transformer.

(ii) For the second case, the transformer is composed of three single-phase units, each rated 35 MVA, 13.8/69 kV, X = 8%. Again, we can calculate the per unit values for voltage and power, which will be 13.8 kV/115 kV = 0.12 pu and 35 MVA/200 MVA = 0.175 pu, respectively. Using the formula for per unit reactance, we get a per unit reactance of 0.08 pu for each single-phase unit.

In both cases, we can see that the per unit reactance for the transformer is the same, despite the different configurations of the transformer. This is because the transformer ratings and voltages are the same, and the per unit system allows for easy comparison and analysis of
 

Related to Transformer and Generator in Per Unit System

1. What is the difference between a transformer and a generator in per unit system?

A transformer is a device that transfers electrical energy from one circuit to another by electromagnetic induction, whereas a generator is a device that converts mechanical energy into electrical energy. In per unit system, both transformer and generator are represented by equivalent circuits with per unit values, allowing for easier comparison and analysis.

2. How is per unit system used in transformer and generator calculations?

In per unit system, all quantities are expressed in terms of their respective base values, such as rated voltage, current, and power. This allows for simplified calculations and analysis, as the values of these quantities remain constant regardless of the actual operating conditions.

3. What is the purpose of using per unit system in transformer and generator analysis?

The use of per unit system in transformer and generator analysis allows for easy comparison and standardization of values, regardless of the actual ratings and operating conditions of the devices. This makes it easier to understand and analyze the performance of these devices.

4. How is the per unit value of a transformer or generator determined?

The per unit value of a transformer or generator is determined by dividing the actual value of a quantity by its base value. For example, the per unit voltage would be calculated by dividing the actual voltage by the rated voltage, and the per unit impedance would be calculated by dividing the actual impedance by the rated impedance.

5. Can per unit system be used for all types of transformers and generators?

Yes, per unit system can be used for all types of transformers and generators, as long as the base values are correctly chosen to represent the operating conditions of the device. However, it is most commonly used for three-phase transformers and generators.

Similar threads

  • Introductory Physics Homework Help
Replies
1
Views
583
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
15K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
4K
  • Introductory Physics Homework Help
Replies
2
Views
785
Back
Top