- #1
Shaun_W
- 320
- 10
Homework Statement
3. Generator G [STRIKE]in the above system[/STRIKE] is a steam turbine driven, 4-pole round rotor synchronous generator and has the following data:
Rated output 250 MVA
Rated Voltage 13.8 kV
Rated frequency 60 Hz
Rated power factor 0.85 lag
Maximum reactive power 140 MVAr
Minimum reactive power -140 MVAr
Impedance data
(to a base of rating)
Calculate
(i) the synchronous speed.
[2]
(ii) the complex power output (P + jQ) when operating at rated conditions.
[4]
(iii) the turbine output torque.
[6]
(iv) if the power output is reduced by 15% calculate the complex power output if the terminal voltage and excitation voltage remain constant.
[10]
(v) if the excitation current is now reduced resulting in a reduction of E by 20% calculate the complex power output if the terminal voltage and active power output remain constant.
[10]
(vi) the theoretical steady state stability limit power available with the parameters of part (v).
[4]
(vii) draw the operating chart for this generator assuming a maximum excitation voltage of 1.9 pu and a 10% stability margin.
[14]
Homework Equations
Just the standard electrical equations, I hope. Although I could be missing something.
The Attempt at a Solution
Part i) was easy enough, I got 1800rpm because N = (120f)/P = (120*60)/4 = 1800rpm.
Part ii) is where I'm stuck. It seems really easy but I think I am missing something. What I think is that S = 250MVA and Q = 140MVAr; therefore P can be found with simple Pythagoras and is 207MW. That sort of makes sense as S x pf should equal the actual power, and 250 x 0.85 = 212, which is fairly close.
Part iii) also seems far too simple to be true. Torque is equal to power x speed, so 207MW x 188rad/s, which equals 39GNm...
I'm a mechanical student and really quite lost.
Thanks for any help.