In summary, you would choose a voltage level, calculate the current drawn from the load, and then calculate the voltage at the source. You would then compare this voltage to the original source voltage. If deviation is over "acceptable %", you would do another iteration.
  • #1
greg997
109
2
Perhaps sb is able to point in the right direction. The task is to calculate the value of the receivig end volatge, for a load of 10 MW at 0.9 pf taken from 66 kV substation.
First I calculated the transmission line impedance
Zlinebase=(Vbase^2)/MVAbase
Zlinebase=132^2/100=174.24Ohm
Zlinepu= 150/174=j0.862
Sbase= 100 MVA
Load impedance = S=P+jQ
S=10+j4.84
Spu=0.1+j0.048 MVA
T1= j0.1 pu and T2= j0.12 pu
So the total impedace = T1+T2+Line+Load= j0.1+j0.2+j0.862+ 0.1+j0.048= 0.1+j1.21 ohm
Is that correct?
I know that the received volatge is Vr= Vs - Voltage drop. But how can I find the voltage drop? I need current for that, so how to find current?
Any help appreciated.According to MATLAB simulation the received voltage shoud be 57kV Line rms. Is that correct?
 

Attachments

  • 1.JPG
    1.JPG
    11.5 KB · Views: 453
Last edited:
Physics news on Phys.org
  • #2
Iteration is one simple an accurate way to solve it.

First of all refer all your values to one voltage level.

Assume 66<0 V at the load, calculate backwards to the source, compare your calculated voltage to the original source voltage. If deviation is large, do another iteration with corrected load voltage. Repeat until deviation is acceptable.
 
  • #3
Could you please show me how to start with it? If I choose the one voltage level to be 132k then what next? And what do you mean by acceptable deviation? If I got 10900 Vs then is it acceptable?Thank you
 
  • #4
There are other methods for solving the problem. If you don't know(or have learned) this method maybe your teacher thinks of another method.

But to help you on the way. I would choose V_load = 66kV<0 at the load.

Calculate the current drawn from the load.

Then calculate the voltage at the source; V_calc = V_load + sqrt(3)* Z*I

Compare this voltage to the original source voltage (ref. 66kV) If deviation is over, let's say 5%, do another iteration.

New voltage at load is: 66kV * V_load / V_calc =

Repeat process until deviation is under "acceptable %".

A bit hard to explain in text but hope you get the picture.
 
  • #5


Based on the information provided, it appears that you have correctly calculated the total impedance of the transmission line, load, and transformers. To find the voltage drop, you will need to use Ohm's law (V=IR) and calculate the current (I) based on the total impedance and the load impedance. Once you have the current, you can use it to calculate the voltage drop across the line using Ohm's law again. The received voltage (Vr) can then be calculated by subtracting the voltage drop from the supply voltage (Vs).

As for the MATLAB simulation, it is difficult to determine if the received voltage of 57kV is correct without knowing the specific parameters and assumptions used in the simulation. It would be best to double-check your calculations and compare them to the simulation results to ensure accuracy. Additionally, it may be helpful to consult with a colleague or supervisor for guidance and to verify your calculations.
 

Related to Received voltage, transmission power system

1. What is received voltage in a transmission power system?

Received voltage refers to the voltage level that is received by the load in a transmission power system. It is the voltage that is measured at the output terminals of the load.

2. How is received voltage calculated?

Received voltage is calculated by taking into account the voltage drop due to the impedance of the transmission line and any other losses in the power system. It can be calculated using Ohm's law (V=IR) or through more complex calculations that consider the power flow and load characteristics.

3. What factors affect the received voltage in a transmission power system?

The received voltage in a transmission power system can be affected by various factors such as the distance between the power source and the load, the impedance of the transmission line, the load characteristics, and any losses in the system. Changes in any of these factors can cause fluctuations in the received voltage.

4. Why is maintaining a stable received voltage important in a transmission power system?

A stable received voltage is important in a transmission power system because it ensures the proper functioning of electrical equipment and appliances. Fluctuations in voltage can cause damage to these devices and affect their performance. It is also important for safety reasons, as high or low voltage levels can pose a risk of electric shock.

5. How is the received voltage regulated in a transmission power system?

The received voltage is regulated in a transmission power system through the use of voltage regulators. These devices adjust the voltage level to maintain a stable output voltage regardless of changes in the input voltage or load. Transformers can also be used to step up or step down the voltage to the required level for the load.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
1
Views
773
  • Engineering and Comp Sci Homework Help
Replies
1
Views
938
  • Engineering and Comp Sci Homework Help
Replies
2
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
2K
  • Electrical Engineering
Replies
6
Views
826
Replies
8
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
15
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
Back
Top