In summary, the conversation discusses the behavior of a synchronous generator when loaded and the return of the rotor to synchronous speed. The generator initially slows down due to a torque imbalance created by the load. However, for a constant input power, the rotor will speed back up and reach synchronous speed again. This is because the power balance is restored either by the prime mover or other machines in parallel. The effect of armature reaction is also mentioned in relation to the rotating electromagnets of the rotor and stator fields.
  • #1
FOIWATER
Gold Member
434
12
Hello,
Assume a synchronous generator is running unloaded and has a fixed input power for any given short time frame (which is a practical consideration for electric power plants). When an electrical load is applied, the machine slows down. I understand this.. what I don't understand is the return of the rotor to synchronous speed. It seems like if you analyze both situations 1) when the synch machine was being rotated at synch speed and 2) when the rotor was being turned at synch speed + delivering electrical energy for the same input power that something doesn't add up?

Thanks
 
Engineering news on Phys.org
  • #2
Why does the generator slow down? Is it because whatever is causing it to rotate it slows down? when power is drawn, whatever is causing it to rotate must supply the mechanical power.
 
  • #3
A simple model.

Think of the grid as an infinitely big AC voltage source at exactly synchronous frequency. Power from the generator to the grid is proportional to the angle difference between the generator and the grid. That angle is the integral of the generator-grid speed difference.

The generators rotor accelerates proportional to the difference in mechanical power in minus electric power out. Increase mechanical power and it will accelerate a bit, making the angle increase, and thus electric power increase. That continues until power in matches power out, and speed matched grid speed once again.

Speed gen = ∫ power in minus power out dt

Angle gen = ∫ Speed gen minus speed grid dt

Power out is proportional to angle gen.

Speed grid is fixed at 60 or 50 hertz.

Equilibrium comes when the rate of change of speed and rate of change of angle are both zero.

If the grid is not infinite it is a bit more complicated, but this is a good approximation.
 
  • #4
I was having trouble understanding why, when a synch. machine is loaded down, it picks it's speed back up following the decrease in speed. I understand why it initially slows down. I do not understand why, for a constant input power, the rotor will speed back up.
 
  • #5
FOIWATER said:
I understand why it initially slows down.

No you don't understand that either.

The answer is in post #2. Please try harder to understand that rather than re-asking the same question. Often, understanding of physics requires some math. A long string of sentences will not clarify as much as a single equation.
 
  • #6
"No you don't understand that either."

The rotating of the field winding causes voltage to be induced in a stationary armature, this voltage opposes the field voltage due to lenz' law. when a load is connected, a current flows which creates a magnetic field opposing the rotating field. For a fixed input power this creates a torque imbalance which causes the rotor to decelerate. I don't understand why upon decelerating, it makes an attempt to accelerate. where does that torque imbalance come from

If you say I don't understand it pin point which part of this is wrong. I appreciate positive feedback.
 
  • #7
OK, I'll give you two hints, then you're on your own.

1) three times you mentioned speed, but you ignored what I said about angle. Angle is the key to understanding synchronous machines.

2) what are the conditions necessary for acceleration/deceleration to cease, and for the power and angle to be steady, either before or after your change in load?
 
  • #8
I'm fine with being "on my own" I will find the answer in a more positive environment

this isn't a case of some one slapping away a helping hand, I appreciate help as much as anyone can but I find intolerance to studious people irrational.
 
Last edited:
  • #9
I am really confused (happens a lot)

Is this a generator or a motor?

If you load a motor it slows down. You want to understand why it speeds back up and stays synchronous?

If you load a generator, the force to keep it rotating increases and the device driving it must supply more power.

I don't understand what you are asking. You ask about a generator, but the questions seem to apply to a motor.

BTW, I too dislike the "I'll force you to learn something because I know more than you and I think you are being lazy" attitude that sometimes prevails here. But you are actually not asking a coherent question.
 
  • #10
I was having trouble understanding why, when a synch. machine is loaded down, it picks it's speed back up following the decrease in speed. I understand why it initially slows down. I do not understand why, for a constant input power, the rotor will speed back up.

Your scenario wasn't thoroughly defined in original post... i think that's at root of the misunderstandings here.

Is your machine in parallel with a lot of others, ie on the grid, or standing alone with its load?

For now, i'll assume the latter.

I do not understand why, for a constant input power, the rotor will speed back up.
Think about that question a moment: Any machine whose output power is more than its input power will slow down as the energy imbalance is made up by expending its rotating inertial energy Iω2.

An electric power plant senses shaft speed, and upon deviation from desired speed very quickly(like as fast as the valves can move) adjusts the mechanical power supplied to generator.
In my plant a 3% speed deviation would have swung mechanical power across its full range of ~800 megawatts in under a quarter second.

So the answer to your question is - the machine will not speed back up unless something restores the power balance. That might be the prime mover, or other machines in parallel.

----------------------------------------------------------------------------------------------

you hinted at an effect known as 'armature reaction' - maybe later ...

But you're on the right track, for to help visualize what's happening you can think of the rotor and stator fields as rotating electromagnets one dragging the other along. Playing with a couple permanent magnets helps one "feel" the elasticity of what in a synchronous machine is called Power Angle" .hoping above helps...old jim
 
Last edited:
  • Like
Likes 1 person
  • #11
Thanks Jim
 

Related to Issue with energy conversion in synch. machine

1. What is energy conversion in a synchronous machine?

Energy conversion in a synchronous machine refers to the process of converting mechanical energy into electrical energy or vice versa. This is achieved through the interaction between the stator and rotor of the machine, which is typically driven by a prime mover such as a turbine.

2. What are some common issues with energy conversion in a synchronous machine?

Some common issues with energy conversion in a synchronous machine include loss of synchronism, unbalanced voltages or currents, and overheating due to excessive loading. These issues can result in reduced efficiency and reliability of the machine.

3. How can loss of synchronism be prevented in a synchronous machine?

Loss of synchronism can be prevented by proper control and monitoring of the machine's excitation and mechanical systems. This includes maintaining a stable power system frequency, ensuring proper synchronization between the machine and the power grid, and performing regular maintenance and inspection of the machine.

4. What causes unbalanced voltages or currents in a synchronous machine?

Unbalanced voltages or currents in a synchronous machine can be caused by unequal distribution of load between the phases, unbalanced magnetic fields due to asymmetry in the machine's construction, or voltage dips or spikes in the power grid. These issues can lead to increased stress on the machine's components and potentially cause damage.

5. How can overheating in a synchronous machine be addressed?

Overheating in a synchronous machine can be addressed by improving the cooling system, reducing the loading on the machine, or performing repairs or replacements on damaged components. It is important to address overheating promptly to prevent further damage and ensure the safe and efficient operation of the machine.

Similar threads

  • Electrical Engineering
2
Replies
37
Views
3K
Replies
1
Views
1K
  • Electromagnetism
Replies
5
Views
416
Replies
19
Views
2K
  • Electrical Engineering
Replies
14
Views
2K
  • Electrical Engineering
Replies
6
Views
3K
  • Electrical Engineering
Replies
6
Views
1K
Replies
35
Views
5K
  • Electrical Engineering
Replies
7
Views
1K
Replies
34
Views
2K
Back
Top