Insulated copper wire turned into gray powder

In summary, the office's owner found an insulated copper cable whose red insulation had turned into gray powder. The black wire is fine, but the red wire is affected. The insulation is swollen at irregular intervals, and the diameter is about 0.5 to 1 millimeter larger than the unaffected sections.
  • #36
Is the conduit wide enough for vermin damage ? My 'ex-Sparky' BIL described mice & rat nibbles thus.
IIRC, he once traced a frequent 'ring main' trip to a gnawed cable beneath a suspended floor. Despite fuse-board's 'safety breaker', the perp died of it. Had the system not tripped repeatedly, prompting timely investigation, the damage may have allowed condensation etc to penetrate...

I've seen similar, if milder damage in a UHF TV aerial's 'coax' down-lead due moisture ingress at abrasion pin-holes. When I removed the plug, the cable 'peed' on me. Stripping it back, I found much mesh shield had turned to greyish dust. Also explained why the distribution amp was 'misbehaving'...

FWIW, I recently had land-line phone service restored after months of intermittent problems. Some days okay-ish, some days dire. But, when I rang the service provider, even though their caller display identified me, my location and my valid account, call handler would not raise a ticket for my 'bad line' because the line was too noisy for him to take all the relevant details.
'Joined-Up Thinking', Not !

In the end, I used the service provider's web forum to plead for help. Which came very, very promptly...
Tech's binary-search revealed one of our cats had chewed the in-house wire in a very obscure place !

(OT: Boss-Cat has figured how to unplug un-shrouded network cables by clawing their tiny clip... )
 
  • Like
  • Haha
Likes diogenesNY, Majorana, Torbert and 2 others
Engineering news on Phys.org
  • #37
Nik_2213 said:
Is the conduit wide enough for vermin damage ?
I don't think so. Inner diameter of the conduit is about 1/2", put the cables in it and imagine how much is left... But especially, remember that the PVC insulation was swollen, but definitely intact!

(OT: Boss-Cat has figured how to unplug un-shrouded network cables by clawing their tiny clip... )
Hats off to Boss-Cat! (and to any kitty/cat/feline as far as I'm concerned =^.^=)
OMINO BIALETTI (r50).png
 
Last edited:
  • Like
Likes Nik_2213
  • #38
I just found a lab to analyze the mystery powder! :cool: They would be available to check a sample in a week, next monday to be precise. Results should follow within two or three days. Stay tuned! ;-)
 
  • Like
Likes Nik_2213, dlgoff, Tom.G and 4 others
  • #39
Good day folks,

the analysis took considerably longer than I had expected, and the results are not as exhaustive as I hoped: the problem was the VERY small amount of powder that I was able to collect. Once I had removed all the pieces of residual solid copper (partially dissolved wire strands) from the powder, the yeld was perhaps less than 50 mg worth of gray powder. ANYWAY, the analysis reported that it was constituted of copper salts only. No trace of any other metals (aluminium...) was found.

Before and after the analysis, I had a bit of brainstorming with a chemical engineer, whose multi-decade experience with the chemistry of metals came in just handy. After a lenghty explanation about the "mystery cable", details of the installation, the bubbles etc etc, he theorized that a number of notable coincidences may have concurred to the degradation of metallic copper into a gray powder.

He supposed that, if the PVC insulation had some (almost)invisible cracks that put the copper strands in contact with the environment; if the environment was not only relatively moist [RH over here lies in the range 60%-85% most of the time] but also alkaline (the floor is made of concrete, so that's quite probable), and if the air was contaminated by certain elements that I can't remember right now (this is a 3.5M inhabitants city located in a very large depression with little natural ventilation, so smog and haze are almost constantly present), then the copper may have reacted with the oxygen and water in the air, and due to the alkaline pH and the other contaminants the outcome was not just the usual greenish-graysh-blackish coat typical of copper, but a complete degradation/disintegration.

It goes without saying that nor him or any of his colleagues had ever seen something like that before...
 
Last edited by a moderator:
  • Like
Likes SredniVashtar, Lord Crc, Asymptotic and 8 others
  • #40
Majorana said:
It goes without saying that nor him or any of his colleagues had ever seen something like that before...
That sounds like a rational speculation. But it sounds like a case where the explanation will never be established with certainty.
 
  • #41
Majorana said:
constituted of copper salts only.
Any (practical) way of finding out which salts?
 
  • #42
None "practical". Because the very small amount of powder in the few "bubbles" left would make further in-depth analysis very hard or impossible at all, AND because (I've been told) the labs out there that perform inorganic chemistry analysis - a tiny minority, since the vast majority are clinical analysis labs - are aimed to testing environmental-protection-related substances, which is not the case here. I guess some University lab could be a good candidate, but I don't have any hooks in there...
 
  • Sad
Likes Tom.G
  • #43
It was a wonderful follow-through for a seemingly minuscule, but actually quite interesting problem :bow:

If you still have the remaining cable then I wonder if you could put it back after violating it a bit? Just some trampling or so.
Maybe together with a printed explanation.
 
  • #44
Rive said:
It was a wonderful follow-through for a seemingly minuscule, but actually quite interesting problem

Yes, "interesting" is the word, if you looked at the pictures... it is a pretty unique case of catastrophic degradation of the conductor. Since it could have happened to theoretically any copper wire/cable in any potentially critical installation (and not just to a silly loudspeaker for ambient music...) I think it's imperative to understand the mechanism behind that.
Rive said:
I wonder if you could put it back

I am not completely sure of what you meant with "put it back", but there is good news for the sake of experimentation. The owner of that workshop has replaced the length of cable that was removed with another identical length taken from the very same roll of cable! 💡🤓The new length of cable has been thoroughly checked inch by inch and was intact at the moment of installation (another proof that the degradation takes place only when the cable is in place, and not just in the same room but over the floor instead of under it...).
Now we have to be patient and wait approximately another 18 months... so by the late spring of 2021 we should know. I wish to kindly ask the admins not to close this thread after a certain time, as it usually happens... :oldbiggrin::angel::oldtongue:
 
  • Like
  • Love
Likes Richard Crane, Tom.G, Klystron and 2 others
  • #45
Sometimes older threads are closed automatically to avoid necroposting, feel free to contact Mentors to reopen the thread if it happens. We will be happy to see how the situation evolves.
 
  • Like
Likes dlgoff, Tom.G and Majorana
  • #46
If copper is left outside in the Sun the copper will harden. If moved after the copper hardens it begins to crack if moved, this is why they make Solid core and Twisted Strand (more stable from cracking) Cat 6 cabling, Solid core needs to be left alone once installed for the cracking reason. If this cable was preinstalled in an area with Windows it is possible that it took a sun hit, was stepped on several times. Just another theory. Many people will step on a cable as they roll it out, then let out some slack, and step on it again. Those spots are more then likely where someone stomped on it.
 
  • #47
bhusebye said:
If copper is left outside in the Sun the copper will harden. If moved after the copper hardens it begins to crack if moved, this is why they make Solid core and Twisted Strand (more stable from cracking) Cat 6 cabling, Solid core needs to be left alone once installed for the cracking reason. If this cable was preinstalled in an area with Windows it is possible that it took a sun hit, was stepped on several times. Just another theory. Many people will step on a cable as they roll it out, then let out some slack, and step on it again. Those spots are more then likely where someone stomped on it.
This cable was sheathed in PVC and under a floor, so sunlight is an unlikely factor.
 
  • #48
I do confirm. The roll of cable came straight from an electronics shop, and was stored in a closet in the office. It never saw any sunlight at all. The same goes for stomping: it was a length of about 6 meters total, of which 4 in the conduit under the floor and 1 out of the floor at each end. It was just cut from the roll and put through the conduit by hand, an 1-minute job.
 
  • #49
Guineafowl said:
This cable was sheathed in PVC and under a floor, so sunlight is an unlikely factor.

Your not understanding. This can also happen if you walk on the cable, even if coated with PVC crap. Think of it this way, when I was a plumber rolling out copper on the ground 3/4 pipe and it sat out in the sun too long, what happens when you go to try to bend it, so it comes up straight in the wall? It kinks is what happens.

I also installed cat 5 and cat 6 cabling, cat 5 would BREAK if you walked on it. And some of it was laying on the ground preinstalled and the links between switches and routers, or switches and another switch or pc would break. Twisted pair even has a coating on it. One substantially less brittle than that Red PVC coating on speaker cable. ANY added HEAT even through CONDUCTIVITY causes copper to get brittle and degrade over time, and when you run cable you tend to step on the wire on the floor not the parts in the wall.

Solid core cat 6 cable you can only install it one time. Over time it gets hard, moving it around will break it because the copper inside solidifies and is no longer pliable, just like the copper pipe, it will kink and break.
Cat 6 stranded you can tie in a knot when you first install it and it will still pass traffic and you can move it around after it is ran. You can't run cat 5 and twist it in a knot, it will not pass traffic.

Excuse me if I did not specifically talk about heat.Edit: post contained a formatting error that made it look like just a quote without any comment and was deleted as such. I have stumbled upon it by chance, corrected formatting and restored.
 
Last edited by a moderator:
  • Like
Likes Nik_2213
  • #50
Not even worth arguing about anymore, my post was deleted and I give up trying to explain to you thermal properties of copper and introduction of breakages that can happen even with that pvc cover which somehow people seem to think is a magic non breakable prophylactic covering.
 
  • #51
The powder is CuCl. PVC is 60% chlorine which provides the catalyst for the change, and the location of the wire provided the environment. The copper wire at some point heated to over 450C and reacted with the chlorine in the PVC. This is much more likely to happen in stranded wire, especially improperly protected stranded wire, as a pinch point or other mechanical force exerted on the wire can cause strands to break inside the sheathing, increasing the wire's resistance and decreasing its heat dissipation.

Interestingly enough, the combination of copper wire and PVC sheathing makes for an effective yet presumably unintentional fail safe. In the event of a runaway overload, the chlorine will react with the copper, opening the circuit before the copper can melt and the other layers of pvc reach its melting point.
 
  • Informative
  • Wow
Likes Tom.G and sysprog
  • #52
ZG1K said:
The powder is CuCl. PVC is 60% chlorine which provides the catalyst for the change, and the location of the wire provided the environment. The copper wire at some point heated to over 450C and reacted with the chlorine in the PVC. This is much more likely to happen in stranded wire, especially improperly protected stranded wire, as a pinch point or other mechanical force exerted on the wire can cause strands to break inside the sheathing, increasing the wire's resistance and decreasing its heat dissipation.

Interestingly enough, the combination of copper wire and PVC sheathing makes for an effective yet presumably unintentional fail safe. In the event of a runaway overload, the chlorine will react with the copper, opening the circuit before the copper can melt and the other layers of pvc reach its melting point.
Interesting possibility, provided that such heating of the copper wire could occur. But the cable was used to connect a SMALL loudspeaker to a SMALL amplifier, to provide background music (i.e. low volume) in a small reception office. The amplifier was not defective (or the loudspeaker coil would have burned loooong before the cable!), both the amplifier and the loudspeaker worked fine after the cable was replaced. No other wires in the vicinity, the loudspeaker cable was the only cable running in that conduit under the floor. Absolutely zero chances that the cable could heat above 40°C.
 
  • #53
Any chance that the PVC was incompletely polymerized leaving som readily available Chlorine? If so, could the CuCl reaction take place at room temp?
 
  • #54
Tom.G said:
Any chance that the PVC was incompletely polymerized leaving som readily available Chlorine? If so, could the CuCl reaction take place at room temp?

Doesn't make much sense chemically. No chlorine in the production of PVC. It it used in an earlier step, during production of a monomer, vinylium chloride - but any excess chlorine left before the monomer is used in polymerization would react with the double bond present, converting the vinylium chloride to just a trichloroethane and rendering it useless for the PVC production.
 
  • Like
  • Informative
Likes David Lewis, Tom.G and sysprog
  • #55
Borek said:
Doesn't make much sense chemically. No chlorine in the production of PVC. It it used in an earlier step, during production of a monomer, vinylium chloride - but any excess chlorine left before the monomer is used in polymerization would react with the double bond present, converting the vinylium chloride to just a trichloroethane and rendering it useless for the PVC production.

PVC (PolyVinylChloride) is C2H3Cl. There is certainly chlorine in it.
 
  • #56
ZG1K said:
PVC (PolyVinylChloride) is C2H3Cl. There is certainly chlorine in it.
Please re-read what @Borek said. He well knows that there's chlorine in PVC and didn't say that there wasn't. He was in an overviewing manner explaining some things about the PVC production process that were relevant to the question.
 
  • Like
Likes Tom.G
  • #57
In the 1960s this was called black wire corrosion because the copper wire that disintegrated was more prevalent in wires with black plastic insulation. A tentative hypothesis put forward was corrosion caused by outgassing from the PVC insulation. It was never corroborated, however.
 
  • Love
Likes Majorana
  • #58
I am wondering if it is an attack by rodents. The copper was then exposed to atmospheric corrosion, maybe from ozone created by photocopiers.
 
  • Skeptical
Likes sysprog
  • #59
tech99 said:
I am wondering if it is an attack by rodents.
Majorana said:
...cable was the only cable running in that conduit
I'm not sure I would even like to know there IS a rodent that big! :eek:
 
  • #60
Tom.G said:
I'm not sure I would even like to know there IS a rodent that big! :eek:
Yes, I suppose the rodent is implausible - I had not previously realize Copper is attacked by Ozone. The biggest rodent is the Capybaras, by the way, which is a lovely animal.
 
  • Informative
  • Haha
Likes Tom.G and Klystron
  • #61
@tech99 @Tom.G jokes apart, it's not a matter of conduit size. The PVC insulation on the affected wire was INTACT, as I explained in the opening post. It was just a little "bulging" (swelling) at the spots where the copper got pulverized, but wasn't chewed nor broken before I cut it longitudinally to extract the powder.
 
  • #62
Majorana said:
Dear all,
thank you so much for all your contributions.

Going backwards:

@Klystron the floor is not a raised floor with plenum, ducts etc. It's an ordinary, old concrete floor, with plastic tubing for electrical wires embedded in it.

@Guineafowl I'm really unable to see your point in sticking with the aluminium idea, despite all the contrary evidence. Until now, I did not want to mention the fact that I am an experienced electronics designer, that I also designed electronics for military aircraft in service nowadays, and that I have handled, stripped and soldered electrical wires of any sort for almost 50 years now, but now I feel obliged. Any scientist knows that trying to shape evidences in order to match a theory leads to faulty results. I know very well that an aluminium wire would explain this phenomenon much easily than a copper wire, but unfortunately this is not the case. I might borrow a camera with macro lens just to post a picture of the cross-section of the copper strands, but I feel that this thing has gone too far.

@anorlunda yes, it's perfectly possible, and in addition the colour of that powder was not perfectly homogeneous. The next step I wish to take would be to have that powder analyzed. It's not so easy to find a lab willing to do the job for a private citizen. In case I find one, I would certainly post the results here, be sure of that.

@Borek as I mentioned a couple of times in my above posts, the two external sections of the cable that did not lie under the floor (they went vertically from the floor to a junction box on the wall on one side, and to the loudspeaker on the other side) are completely normal and unaffected, as well as a length of excess cable left over after installation and stored in a drawer in the same office.

Something similar happened to me with a cable, It turned into grey power, but it hadn't been in use for a long time. The cable remained in a house that is on the beach, so there is high humidity and salinity that accelerate corrosion. In my case it was as @Guineafowl mentioned. The sections that still had wires, at first sight seemed like copper, however, when I scratched them, the silver color came out. Perhaps the humidity and salinity affected the alloy of copper with aluminum.
 

Attachments

  • 1.jpg
    1.jpg
    46.6 KB · Views: 186
  • 2.jpg
    2.jpg
    23 KB · Views: 174
  • 3.jpg
    3.jpg
    74.3 KB · Views: 228
  • 4.jpg
    4.jpg
    83.5 KB · Views: 372
  • Informative
  • Like
Likes Majorana and Keith_McClary
  • #63
In a very similar vein, yesterday I was using some very old clip leads (25-30 yrs.) when a clip came off of one. Didn't think to bother with photos but it reminded me that I had seen the bright green wire corrosion before but couldn't place it (oily and the color of Copper Sulfate).

Cutting off a couple inches and stripping the wire back disclosed the same corrosion, again reminding me I had seen it before.

Conclusion/speculation is that the vinyl insulation had something in it that reacted with the Copper. Other clip leads stored in the same box did not show any corrosion.

Cheers,
Tom
 
  • #64
Carol said:
Something similar happened to me with a cable, It turned into grey power, but it hadn't been in use for a long time. The cable remained in a house that is on the beach, so there is high humidity and salinity that accelerate corrosion. In my case it was as @Guineafowl mentioned. The sections that still had wires, at first sight seemed like copper, however, when I scratched them, the silver color came out. Perhaps the humidity and salinity affected the alloy of copper with aluminum.
Carol, you got it! 👍 My wires look exactly the same way (although corrosion was perhaps more "complete" in my case, but I guess it's just a question of time...)
In my case, the environment is completely different from that of a beach house: large city, hundreds of kilometers from the sea, no construction works in the vicinity. But yes, the climate is generally damp, although not saline.
 
  • #65
I installed after market power door locks on my chevy 1500.
Wound up a year later with same problem All colors red blue green brown white purple black orange all did it.
Thanks for finally finding somewhere to explain.
 
  • Like
Likes Majorana
  • #66
I had a set of jumper cables that appeared to be copper (they were copper plated alumimum), I had a lot of problems with them and the conductors corroding off the clamps
 
  • #67
FWIW, I'll mention this. Another person on the debian-user@debian.org mail list found this web page, which is relevant to some discussions on that list. I'll cite one post as an example: https://lists.debian.org/debian-user/2023/06/msg00081.html.

The gist is that one debian user in particular (the author of that message) has found, over a long period of time, lots of similar problems with cables that he describes as cables with "hot red" (magenta) cable insulation, extending back from the days when there was typically a red lead leading to a microphone (I'm not clear if that was in CB sets, or more like TV (or radio) broadcast sets), and extending to SATA cables up to almost today. (Users who are cognizant of the problem make it a practice to use SATA cables that are some color other than red.) (Maybe the problem is gone in SATA 3 cables?)

If I was less lazy, I'd try to dig out more of the relevant posts, but I am old and lazy :-(

I decided to just present this as a data point and maybe a hint that might lead to collaboration / further investigation / understanding of the problem.

Oh, he describes it as a rust colored powder, I don't know if that might be also seen as sort of a dark gray...
 
Last edited:
  • Informative
  • Love
Likes Majorana and Tom.G
  • #69
rhk01 said:
FWIW, I'll mention this. Another person on the debian-user@debian.org mail list found this web page, which is relevant to some discussions on that list. I'll cite one post as an example: https://lists.debian.org/debian-user/2023/06/msg00081.html.

The gist is that one debian user in particular (the author of that message) has found, over a long period of time, lots of similar problems with cables that he describes as cables with "hot red" (magenta) cable insulation, extending back from the days when there was typically a red lead leading to a microphone (I'm not clear if that was in CB sets, or more like TV (or radio) broadcast sets), and extending to SATA cables up to almost today. (Users who are cognizant of the problem make it a practice to use SATA cables that are some color other than red.) (Maybe the problem is gone in SATA 3 cables?)

If I was less lazy, I'd try to dig out more of the relevant posts, but I am old and lazy :-(

I decided to just present this as a data point and maybe a hint that might lead to collaboration / further investigation / understanding of the problem.

Oh, he describes it as a rust colored powder, I don't know if that might be also seen as sort of a dark gray...
Thank you so much, that is *VERY* interesting!

"replace any "hot red" aka "magenta" sata cable with some other color. I am a CET and known to me since the 1970's, that color of insulation dye will in time, convert the copper of the conductor into a rust colored powder, and that is a poor conductor"

It definitely looks like the same deterioration I observed on my cable in 2019!
 
  • #70
rhk01 said:
If I was less lazy, I'd try to dig out more of the relevant posts, but I am old and lazy :-(
I should mention that that person (Gene Heskett) has reported on that problem on that list over a long period of time -- if someone goes looking for his posts on that subject, you may have to look back as far as 10 years or more. (He is a prolific poster, and you will also find a lot of posts not relevant to the problem.)

The only thing I can think of off the top of my head that might be gained by looking for his old posts might be to clarify what kind of microphone sets he found the problem in (CB, or TV (or radio) broadcast sets, or maybe both), and other red cables he might have found the problem in.

Oh, and I might add, the other lead(s) to the microphone (in other colored insulation) were not affected by the problem.
 