Floating Earth leads to dangerous case voltages - neutral OK

In summary: You have a very dangerous condition now, because if the supply is reversed, say the socket is wrongly wired, the metal case will be connected to live. I suggest you need to remove the neutral link shown under the transformer and ensure the ground connection is 100%. Ensure you have a double wound transformer, not an auto transformer i.e. one with one winding with a tap.
  • #1
gbell
7
0
I moved to Australia from the US and took my Crate amp and Ibanez electric guitar with me. To deal with the 240 VAC, I needed a step-down transformer. So I have this setup:
guitar.png

The ground connector of the socket on the 120 VAC side got weak and stopped making connection (Note 1). So the guitar floated. Problem is, I feel a mild shock when I'm touching a metal part of the guitar with my bare foot resting on the metal case of my PC (I live an exciting life).

If I measure that voltage (Note 2), it's north of 100 VAC sometimes. Should an open ground cause this? What piece of equipment is at fault and how do I fix it? I'm unnerved that a simple open ground caused a voltage so high.

The house's bond between neutral and ground is nearby and I'm sure it's good - I've just had it re-done and tested.

Help much appreciated.
 
Last edited:
Engineering news on Phys.org
  • #2
gbell said:
I moved to Australia from the US and took my Crate amp and Ibanez electric guitar with me. To deal with the 240 VAC, I needed a step-down transformer. So I have this setup:
https://www.physicsforums.com/attachments/82803
The ground connector of the socket on the 120 VAC side got weak and stopped making connection (point A). So the guitar floated. Problem is, I feel a mild shock when I'm touching a metal part of the guitar with my bare foot resting on the metal case of my PC (I live an exciting life).

If I measure that voltage (at point B), it's north of 100 VAC sometimes. Should an open ground cause this? What piece of equipment is at fault and how do I fix it? I'm unnerved that a simple open ground caused a voltage so high.

The house's bond between neutral and ground is nearby and I'm sure it's good - I've just had it re-done and tested.

Help much appreciated.
You have a very dangerous condition now, because if the supply is reversed, say the socket is wrongly wired, the metal case will be connected to live. I suggest you need to remove the neutral link shown under the transformer and ensure the ground connection is 100%. Ensure you have a double wound transformer, not an auto transformer i.e. one with one winding with a tap.
 
  • #3
Your use of “A” on an Earth lead is confusing since it is the symbol for Active.
In Australia the 240VAC is provided by a common neutral with a single active phase.
Your circuit also has an Earth connection that you must repair to make things safe.

The 240VAC is symmetrical about the neutral conductor, so you can expect capacitive coupling to produce about half the 240VAC = 120VAC on the ungrounded chassis. There is little power behind that floating voltage. It is the high impedance of your DMM that is detecting the voltage. That does not mean that it is not a problem. Voltage can damage insulation and cause power supply failures.

The link across the transformer is not a problem, do not remove it. It keeps the voltage of the secondary within range of the primary and so breakdown potential to Earth is not exceeded.

You must repair your Earth connection between the wall, the external transformer and the amplifier chassis.
 
  • #4
gbell said:
Should an open ground cause this?
Very likely it would. A Baluncore pointed out, a tiny current flows through your amp into the guitar and your DMM and your foot are both sensitive enough to detect it. That current needs to be intercepted and returned to Earth by the "ground connection" at your Note 1.

gbell said:
What piece of equipment is at fault and how do I fix it?
You already said it's the socket on the 120VAC side of the transformer. Replace it.

gbell said:
The ground connector of the socket on the 120 VAC side got weak and stopped making connection (Note 1). So the guitar floated. Problem is, I feel a mild shock when I'm touching a metal part of the guitar with my bare foot resting on the metal case of my PC (I live an exciting life).
You've shifted tense here, past to present. .
Are you saying you've already fixed the socket but still have the problem ? I'm confused.

If your question is ,
'why does my (now) grounded amp still shock me?' ,
you should make this test:

1. Unplug amp from transformer.

2. Connect DMM leads :
one to the ground prong of amp's power cord
other to metal on guitar

3. select DMM to ohms
if you do not read almost zero, then your amp is not providing the "ground" connection that you think it is. That bottom wire in your sketch isn't right.

If you do read almost zero,
4. .string a long wire out the window to your house ground rod . Use that for "ground" and measure voltages from there to inside receptacles' ground point., to case of your PC, and to guitar .
http://www.thearrivalstore.com/media//Type_I.JPG
who knows - it could be your PC or the house service panel itself.
 
Last edited by a moderator:
  • #5
Baluncore said:
Your use of “A” on an Earth lead is confusing since it is the symbol for Active.
Agreed, thanks. Have modified the diagram.

so you can expect capacitive coupling to produce about half the 240VAC = 120VAC on the ungrounded chassis.
Interesting, that explains it. Does it make sense that I can easily feel it though? Jim (below) thinks so. I understand the high-impedance of the DMM picking it up, but my impedance is quite a bit lower. It feels strong enough to be nearly dangerous. Wouldn't this situation have been common before they started grounding chassis?
 
  • #6
jim hardy said:
You already said it's the socket on the 120VAC side of the transformer. Replace it.
So that one fault is enough to explain the phenomenon, and the strength of what I'm feeling (subjective, sorry) doesn't indicate anything more serious.

You've shifted tense here, past to present.
The fault HAPPENED and NOW I can feel the described effects. I have not yet fixed the ground.

who knows - it could be your PC or the house service panel itself.
Measured voltages to the socket, so it's not anything special with the PC (good point). And it's not the house panel because I've had a good electrician over here checking things and re-doing the house earthing (as mentioned).

So the consensus seems to be: Capacitive coupling explains the measured voltage and the felt effect. Earthing isn't just for safety in case a fault makes the case live, but also to eliminate this coupled voltage - desirable to prevent insulation breakdown, for comfort/sanity and possibly safety if the current is high enough.
 
  • #7
gbell said:
I have not yet fixed the ground.
Thanks for the clarification.

one step at a time. Hopefully that'll fix it.
 
  • #8
gbell said:
It feels strong enough to be nearly dangerous. Wouldn't this situation have been common before they started grounding chassis?
Chassis have always been grounded to protect the transformer insulation. Originally the Earth used was the water pipes in a house, that was replaced by providing an Earth terminal on power outlets. A good Earth increases the chance that a fuse will blow before the live chassis kills someone.

Voltage is always dangerous, it kills when the current rises sufficiently to trigger muscular activity. The human body can sense very small currents. I can best sense 50Hz AC on floating equipment by brushing it with the top of my fingers. When I do sense AC, I always identify the leakage and fix the Earthing system.

With a good Earth, if the leakage current is sufficient then it should trigger your structure's residual current protection, RCD. You will then know that the AC insulation of your amplifier has broken down and needs repair.

You know there is an Earthing problem. Failure to fix the known faulty equipment represents the legal liability of a manslaughter charge, with a period of imprisonment or a coffin for you. You must get the Earth connection fixed before you continue to use the equipment.
 
  • #9
Baluncore said:
Chassis have always been grounded to protect the transformer insulation.
In the days of two-pronged outlets, was the chassis just tied to neutral?

With a good Earth, if the leakage current is sufficient then it should trigger your structure's residual current protection, RCD.
I have RCDs. They're not triggering on this, presumably because of the isolation provided by the step-down transformer?
 
  • #10
gbell said:
In the days of two-pronged outlets, was the chassis just tied to neutral?
No. There is not always a neutral for a two wire system, and the Active and Neutral often get swapped in the plug. In the USA for example, both conductors could be live and symmetrical about Earth, so the electric field tended to cancel toward zero. Those two wires are twisted together so the magnetic field due to the current flow also cancels toward zero.

gbell said:
I have RCDs. They're not triggering on this, presumably because of the isolation provided by the step-down transformer?
It is not an “isolation transformer”. The link across the step-down transformer enables a fault on the amplifier side between Active and Earth to trigger the RCD. The link also prevents high voltage breakdown of the stepdown and amplifier transformer's insulation.

An RCD looks at the difference between the Active and Neutral currents. When that AC current exceeds 30 mA it will isolate the circuit. The typical way to get a difference is to have a current from active to ground. That will happen if you accidentally cut through a power cord because the Active in the cable may short to the Earth = RCD, or to the Neutral = current limit fuse or Circuit Breaker.

Your leakage current is probably well below the 30 mA RCD threshold.
 
  • #11
gbell said:
In the days of two-pronged outlets, was the chassis just tied to neutral?
Hmmmm, well, sometimes.

Two prong plugs nowadays have one wide and one narrow blade so they'll only go in one way but that was not always the case.
Those old radios from 1930's to 1950's , the cheap table models in plastic or wood cases often were wired as you suggest.
They were called "All American Fives" because they all used the same 5 tubes.
AllAm5.png
AA5sch.png



To make them cheap they didn't have a power transformer. One side of the line cord was tied to chassis, and the enclosure was supposed to keep you from getting shocked. Before 1950's the plug was not polarized and could go in either way, so the chassis might be connected to either hot or neutral.

http://en.wikipedia.org/wiki/All_American_Five
Potential hazards of the design
Many early examples of the 'All-American Five' posed a shock hazard to users. Lacking a mains transformer, the chassis of the AA5 radio was directly connected to one side of the mains electric supply. The hazard was made worse because the on/off switch was often in the wire of the mains supply which was connected to the chassis, meaning that the chassis could be "hot" when the set was either 'on' or 'off', depending on which way the plug was inserted in the power outlet. Many power plugs had two identical pins, and could be plugged in either way round. The metal chassis securing screws were sometimes accessible from the outside of the Bakelite or wood case, and there were many examples of owners receiving a shock by making contact with these screws while handling a set. Ventilation holes could be large enough to allow children to poke their fingers, or metal objects, through. The same type of hazard was present in European AC/DC sets, at twice the voltage.

Better equipment like quality console radios and TVs always had a hefty power transformer that isolated chassis from house power.

........ boring anecdote...

My freshman year a guy in a room down the hall had a really nice stereo by 1964 standards.
But no tuner, just a turntable. That was not uncommon then for FM stereo was relatively new as was transistor Hi-Fi
He and his roommate scrounged a couple of "All American 5's" and decided they'd run wires from their speaker terminals to the aux inputs on the stereo. That'd give them big sound. In those days "Clear Channel" AM radio was popular and broadcast rock 'n roll music nationwide at night. In central Missouri we could get AM stations sometimes as far away as Quebec.

Their hookup worked okay the first time. They'd got lucky and plugged in both radios with chassis at neutral.
But they unplugged one radio to resolder a wire, and when they plugged it back in the plug was other way. Needless to say it made a lot of sparks, noise and smoke and scared the daylights out of them.
I think the stereo survived. Tubes are tough.
Things are safer today. If you tinker with an antique radio , be aware of a likely shock hazard.
.
 
  • #12
Thanks for all the info guys. For the record, I replaced the socket and the "effect" is gone. Now, no more excuses for not practicing...
 

Related to Floating Earth leads to dangerous case voltages - neutral OK

1. What is a "floating Earth" and how does it lead to dangerous case voltages?

A "floating Earth" is a situation where the Earth connection in an electrical circuit is not properly grounded. This can happen when a wire or connection is loose, damaged, or missing. When this occurs, the voltage in the circuit can become imbalanced, leading to dangerous case voltages. These can occur when a person comes into contact with an appliance or device that has a missing or damaged Earth connection, resulting in an electric shock.

2. How can I tell if there is a floating Earth in my electrical circuit?

One way to determine if there is a floating Earth in your electrical circuit is to use a multimeter to measure the voltage between the Earth connection and a known Earth reference point, such as a grounded metal object. If there is a significant difference in voltage, it could indicate a floating Earth. Additionally, if you experience electric shocks when using an appliance or device, it could be a sign of a floating Earth.

3. Can a floating Earth be fixed?

Yes, a floating Earth can be fixed by identifying and repairing any damaged or loose wires or connections in the electrical circuit. It is important to hire a licensed electrician to properly diagnose and fix the issue, as working with electricity can be dangerous.

4. Is a floating Earth the same as an open ground?

No, a floating Earth and an open ground are not the same. An open ground occurs when the Earth connection in an electrical circuit is completely missing, while a floating Earth refers to a situation where the Earth connection is not properly grounded. Both can result in dangerous case voltages, but they require different methods of repair.

5. Can a floating Earth cause damage to appliances and devices?

Yes, a floating Earth can cause damage to appliances and devices by creating an imbalance in the voltage in the circuit. This can result in electrical surges or fluctuations, which can damage sensitive electronic components. It is important to have a properly grounded Earth connection to protect your appliances and devices from potential damage.

Similar threads

Replies
19
Views
690
  • Electrical Engineering
3
Replies
83
Views
4K
Replies
13
Views
4K
Replies
6
Views
2K
  • Electrical Engineering