In summary, the conversation revolves around verifying the accuracy of a solution for relating secondary current to primary voltage in a single-phase transformer with resistive load for non-ideal situations. The equations involved include KVL, voltage across a resistor and inductor, and AC voltage as a sine wave. The concept of reluctance and Faraday's law are also mentioned. The attempt at a solution involves solving a system of differential equations and considering mutual inductance, coupling coefficient, and factors such as loading, leakage inductances, and winding resistance. The conversation also highlights the use of phasors and the distinction between inductance and resistance.
  • #1
ZenSerpent
29
0
mod note: thread moved from technical forum so template is missing

Homework Statement


Relate secondary current to primary voltage in a single-phase transformer having resistive load for non-ideal situation.

Homework Equations


KVL, Voltage across resistor and inductor, ac voltage as a sine wave, reluctance, Faraday's law,other equations relevant to working principle of transformer.

The Attempt at a Solution


Good day everyone! I would like to verify whether my attempt for relating secondary current to primary voltage in a single-phase transformer having resistive load is correct or not. Are there other losses that I have not taken into account? If so, feel free to critique my work. This is actually a work of my colleagues and I for our research. So here's our go at it:Using KVL for the equivalent circuit in the primary side gives,[tex] v_1=v_{R_1}+v_{L_1} [/tex]Substituting their corresponding values gives

[tex]v_{1max}{\mathrm{sin} \omega t\ }=i_1R_1+L_1\frac{di_1}{dt}[/tex]Solving DE for [itex] i_1 [/itex] gives

[tex] i_1=\frac{v_{1max}}{R^2_1+{{\omega }^2L}^2_1}\left(R_1{\mathrm{sin} \omega t\ }-\omega L_1{\mathrm{cos} \omega t\ }\right)\ [/tex]Combining the sine wave and cosine wave and simplifying gives

[tex] i_1=\frac{v_{1max}}{\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{sin} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\ [/tex]Now since [itex] N_1i_1=\mathcal{R}\mathrm{\Phi }\ [/itex], solving for [itex] {\Phi } [/itex] gives

[itex] \mathrm{\Phi }=\frac{N_1i_1}{\mathcal{R}}\ [/itex]. This is the flux that flows to the secondary circuit after applying reluctance of the core.
Substituting [itex] i_1=\frac{v_{1max}}{\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{sin} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\ [/itex] to [itex] \mathrm{\Phi }=\frac{N_1i_1}{\mathcal{R}}\ [/itex] gives[tex] \mathrm{\Phi }=\frac{N_1v_{1max}}{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{sin} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\ [/tex]

To determine the flux linkage in the secondary winding, we multiply N2 to both sides, giving[tex] N_2\mathrm{\Phi }=\frac{N_2N_1v_{1max}}{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{sin} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\ [/tex]Taking derivative wrt t gives the voltage across the secondary circuit. That is,[tex] v_2=N_2\frac{d\mathrm{\Phi }}{dt}=\frac{N_2N_1v_{1max}\omega }{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{cos} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\ [/tex]Using KVL on the secondary circuit, we get[tex] v_2=v_{R_2}+v_{R_L}+v_{L_2}\ [/tex]Substituting their corresponding values give,[tex] \frac{N_2N_1v_{1max}\omega }{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{cos} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }=i_2R_2+i_2R_L+L_2\frac{di_2}{dt}\ [/tex][tex] \frac{N_2N_1v_{1max}\omega }{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}}{\mathrm{cos} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }=i_2(R_2+R_L)+L_2\frac{di_2}{dt}\ [/tex]Solving DE for [itex] i_2 [/itex] gives,

[itex] i_2=\frac{N_2N_1v_{1max}\omega }{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}\left[{\left(R_2+R_L\right)}^2+{\omega }^2L^2_2\right]}\left[\left(R_2+R_L\right){\mathrm{cos} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }+\omega L_2{\mathrm{sin} \left(\omega t-{\mathrm{arctan} \frac{\omega L_1}{R_1}\ }\right)\ }\right]\ [/itex]Combining the sine and cosine waves gives and simplifying gives,

[tex] i_2=\frac{N_2N_1v_{1max}\omega }{\mathcal{R}\sqrt{R^2_1+{\omega }^2L^2_1}\sqrt{{\left(R_2+R_L\right)}^2+{\omega }^2L^2_2}}{\mathrm{sin} \left\{\omega t+{\mathrm{arctan} \left[\frac{R_1\left(R_2+R_L\right)-{\omega }^2L_1L_2}{R_1\omega L_2+\left(R_2+R_L\right)\omega L_1}\right]\ }\right\}\ }\ [/tex]
Critiquing this will be of great help for our group's thesis. Thank you so much. :)
 
Last edited:
Physics news on Phys.org
  • #2
ZenSerpent said:
mod note: thread moved from technical forum so template is missing

Homework Statement

[/B]
Relate secondary current to primary voltage in a single-phase transformer having resistive load for non-ideal situation.
[tex] v_1=v_{R_1}+v_{L_1} [/tex]
If L1 is the primary inductance then you're off to a bad start. Or you need to show a diagram of your non-ideal transformer, identifying these parameters.

I would start with basic equations for your transformer:

v1 = L1 di1/dt + M di2/dt
v2 = M di1/dt + L2 di2/dt

L1, L2 are primary & secondary inductances
M = mutual inductance (have you considered this?)
v1, v2 = pri & sec voltages
i1, i2 = pri & secondary currents

and work from there. These equations accommodate loading, leakage inductances, winding resistance, etc.

If you want to include consideration of core fluxes see my Insight article at https://www.physicsforums.com/insights/misconceiving-mutual-inductance-coefficients/
 
  • #3
Thanks Sir rude man. Basing from your comment,

v1 = L1 di1/dt + M di2/dt
v2 = M di1/dt + L2 di2/dt


This implies that this is a system of DE and I need to solve for the corresponding functions of i1 and i2 as functions of time, right? As for the v1 and v2, shall I express them explicitly in the form v = vmax sin(ωt + θ)? I think this would be impossible for i2 since I don't know its phase angle yet.

M = mutual inductance (have you considered this?)
Well Sir, you can see in the last equation the following term N1*N2/R which is equal to μ*N1*N2*A/l. Is this not equal to [itex]\sqrt{L_1L_2}[/itex]? I may be wrong. I don't know.

"These equations accommodate loading, leakage inductances, winding resistance, etc."
How are these inductances related to resistance? Is there an explicit formula expressing the relationship among these variables?

P.S. I'm an Applied Mathematics student, not an Engineering one. But I'm studying this field for our research. Thanks in advance. :)
 
  • #4
ZenSerpent said:
Thanks Sir rude man. Basing from your comment,
v1 = L1 di1/dt + M di2/dt
v2 = M di1/dt + L2 di2/dt

0
This implies that this is a system of DE and I need to solve for the corresponding functions of i1 and i2 as functions of time, right? As for the v1 and v2, shall I express them explicitly in the form v = vmax sin(ωt + θ)? I think this would be impossible for i2 since I don't know its phase angle yet.
Let's assume an input voltage V = V0sin(wt), then a series resistor R1 connected to the transformer primary v1, then a load resistor R2 across the secondary v2. Then the equations would be
(V - v1)/R1 = i1
v1 = L1 di1/dt + M di2/dt
v2 = M di1/dt + L2 di2/dt
v2 = -i2. (I hope this last answers your question about i2.)

4 independent equations, 4 unknowns. Solve classically or, preferably, using phasors which I guess you haven't covered.
M = mutual inductance (have you considered this?)
Well Sir, you can see in the last equation the following term N1*N2/R which is equal to μ*N1*N2*A/l. Is this not equal to [itex]\sqrt{L_1L_2}[/itex]? I may be wrong. I don't know.
. M = k√(L1 L2) and I don't see the "k" which is the coupling coefficient and affects mutual inductance. I believe you assumed unity coupling (all primary flux coupling into the secondary). This is close to true for a power transformer with its high-permeability core, but for (for example) an IF radio transformer it's far from true.

I will try to find time to pay more attention to your rather extensive (and impressive!) post.
"These equations accommodate loading, leakage inductances, winding resistance, etc."
How are these inductances related to resistance? Is there an explicit formula expressing the relationship among these variables?
Inductances L1 and L2 are the inductances of the primary & secondary windings respectively and have no direct relationship to the respective winding resistances.
P.S. I'm an Applied Mathematics student, not an Engineering one. But I'm studying this field for our research. Thanks in advance. :)
You can certainly use classical calculus to solve these equations, though phasors are preferred since they change the diff. eqs. to algebraic ones. But you do need at least basic circuit analysis to do anything with the equations I provided.

Have you looked at my Insight paper? You need not be concerned with the main topic but I do relate electrical parameters to magnetic ones which may be of interest to you.
 
  • #5
For this set of equations,

(V - v1)/R1 = i1
v1 = L1 di1/dt + M di2/dt


Are you trying to say that
(V0sin(wt) - L1 di1/dt + M di2/dt)/R1 = i1, right? So V and v1 are actually different? If V is the input voltage, then what is v1?

Also, I said this statement:

I think this would be impossible for i2 since I don't know its phase angle yet.
I'm actually referring to v2 instead of i2. I apologize for that.

And for this equation:
v2 = -i2
Why is this so? I don't understand. I mean, they don't even have the same units. Are you referring to their respective magnitudes only?

M = k√(L1 L2) and I don't see the "k" which is the coupling coefficient and affects mutual inductance. I believe you assumed unity coupling (all primary flux coupling into the secondary). This is close to true for a power transformer with its high-permeability core, but for (for example) an IF radio transformer it's far from true.
Well, for this Sir, the result excluding k just surfaced from my derivations. Probably it is due to my assumption above that after reluctance is divided to the mmf, the resulting flux will link to the secondary side.

Have you looked at my Insight paper? You need not be concerned with the main topic but I do relate electrical parameters to magnetic ones which may be of interest to you.
I did, and you came up with the equation M = √(k1k2L1L2) which is pretty interesting. How do I know the values for k's?
 
  • #6
ZenSerpent said:
For this set of equations,

(V - v1)/R1 = i1
v1 = L1 di1/dt + M di2/dt


Are you trying to say that
(V0sin(wt) - L1 di1/dt + M di2/dt)/R1 = i1, right? So V and v1 are actually different? If V is the input voltage, then what is v1?
you're a bit sloppy with a sign here, but otherwise yes. V is the input voltage to resistor R1 in series with the transformer primary. v1 is the transformer primary voltage (the low end of both primary & secondary assumed grounded). Sorry I can't draw a diagram right now so go with what I described earlier.
Also, I said this statement:
I think this would be impossible for i2 since I don't know its phase angle yet.
I'm actually referring to v2 instead of i2. I apologize for that.
still don't see what your problem is . 4 equations, 4 unknowns. You are solving for all four of them and v2 is one of them.
And for this equation:
v2 = -i2
Why is this so? I don't understand. I mean, they don't even have the same units. Are you referring to their respective magnitudes only?
That was a big old blooper! I meant to write v2 = -R2 i2. R2 is a resistor across the secondary winding (the transformer load).
M = k√(L1 L2) and I don't see the "k" which is the coupling coefficient and affects mutual inductance. I believe you assumed unity coupling (all primary flux coupling into the secondary). This is close to true for a power transformer with its high-permeability core, but for (for example) an IF radio transformer it's far from true.
Well, for this Sir, the result excluding k just surfaced from my derivations. Probably it is due to my assumption above that after reluctance is divided to the mmf, the resulting flux will link to the secondary side.
yes I think that was the assumption which is fine for a power transformer and certain others having relatively high-permeability cores so that the flux is well confined to the intended magnetic path.
Have you looked at my Insight paper? You need not be concerned with the main topic but I do relate electrical parameters to magnetic ones which may be of interest to you.
I did, and you came up with the equation M = √(k1k2L1L2) which is pretty interesting. How do I know the values for k's?
That depends on how the transformer is manufactured. For most transformers k1 and k2 are the same or closly the same so there is just one coupling coefficient and then M = k√(L1 L2). For power transformers, even small ones, k ~ 1.0.
 
  • #7
Since you apparently want a steady state solution, there's no need to solve differential equations. Using the Laplace variable s, a mesh solution can be simply obtained:

NonIdeal.png
 
  • #8
The Electrician said:
Since you apparently want a steady state solution, there's no need to solve differential equations. Using the Laplace variable s, a mesh solution can be simply obtained:

View attachment 112324
Knowledge or application of the Laplace transform is not necessary if the steady-state, sinusoidal solution is sought. Phasors suffice. But the OP is probably not familiar with phasors either, he/she stating that he/she is not an engineering but an applied math student. So classical calculus is probably his/her only way to go.
 
  • #9
Sirs, I already figured it out. But the equations really looked very hideous. I may be able to post it later.
 
  • #10
The Electrician, may I know what the initial equations looked like before they were set up in the matrix and before their Laplace transforms were taken? I also have a somehow considerable understanding of Laplace transforms and transfer functions btw, Sirs, but not that deep enough.
 
  • #11
There's no need to perform any Laplace transforms to perform steady state AC circuit analysis.

See this page just beyond half way down, under the section heading "Generalized s-plane impedance" at this page: https://en.wikipedia.org/wiki/Electrical_impedance. The variable s can be taken to be simply jω for AC circuit analysis.

Then read this page: https://en.wikipedia.org/wiki/Mesh_analysis for a short overview of the technique of phasor mesh analysis.

The two mesh equations are:

1.) (s*L1+R1)*I1 + (-s*M)*I2 = V1
2.) (-s*M)*I1 + (s*L2+R2+RL)*I2 = 0

The minus sign in the term "-s*M" is there because of the dotted ends of the transformer windings. If one of the dots were on the other end of the winding, the sign would be changed.

In post #8, I showed the equations in matrix form, which allows the use of a matrix solver to obtain the solution. But any technique for solving a pair of simultaneous linear equations can be used.
 
  • #13
The Electrician, I now understand what you're trying to say and I tried so solve them manually. Luckily, I got the same answer for the magnitude and angle.
If we translate this back in the t-domain, will i(t) = L^(-1){V1(s)}*(magnitude derived)*sin(wt + (angle derived)) or i(t) = V1max*magnitude derived* sin(wt + (angle derived)) or should the phase angle be negative? Thanks.
 
  • #14
ZenSerpent said:
The Electrician, I now understand what you're trying to say and I tried so solve them manually. Luckily, I got the same answer for the magnitude and angle.
If we translate this back in the t-domain, will i(t) = L^(-1){V1(s)}*(magnitude derived)*sin(wt + (angle derived)) or i(t) = V1max*magnitude derived* sin(wt + (angle derived)) or should the phase angle be negative? Thanks.

The phase of the current with respect to the applied voltage is delayed, as you would expect in an inductor, but the current in the secondary of your transformer will experience a possible additional 180° phase shift depending on where the windings are dotted: https://en.wikipedia.org/wiki/Polarity_(mutual_inductance)
 
  • #15
How about if it is dotted the same way as you did in formulating the initial equations?

And what will the equation in the time domain will look?
 
  • #16
ZenSerpent said:
How about if it is dotted the same way as you did in formulating the initial equations?

Substitute some values for L1, L2, M, R1, R2, RL and ω into the expression I obtained for I2/V1:

Tmp1.png


and find the angle of the result. If the dot on one winding of the transformer is reversed, then substitute M = -M and re-evaluate the expression.

ZenSerpent said:
And what will the equation in the time domain will look?

This is your homework, not mine. What do you get for the time domain equation? I see a zero and a couple of poles in the expression, so I would expect a moderately complicated time domain expression.
 
  • #17
IMG_1486012782.791948.jpg


I got this answer. Is this acceptable?
 
  • #18
Sir, also noticed that the answer is not in Amperes.
 
  • #19
Oops. I forgot the convolution theorem.
 
  • #20
ZenSerpent said:
View attachment 112408

I got this answer. Is this acceptable?

This is not the steady state result. You will note that you have a decaying exponential factor. What you have is the result of suddenly applying a sine wave at t=0. Get rid of the exponential factor and the remaining part should be the steady state result.

But you already have the steady state result in phasor format. Why have you bothered to invoke Laplace transforms?
 
  • #21
The Electrician said:
This is not the steady state result. You will note that you have a decaying exponential factor. What you have is the result of suddenly applying a sine wave at t=0. Get rid of the exponential factor and the remaining part should be the steady state result.

But you already have the steady state result in phasor format. Why have you bothered to invoke Laplace transforms?

So the expression outside the brackets is the answer?

I applied LT since I need it to be in the time domain. Is there something wrong in doing it?
 
Last edited:
  • #22
You're making me do a lot of work here. Let me explain why using phasor analysis saves a lot of work, and is the right way to do things when you want a steady state result. I'm going to use Mathematica to do a lot of the work involved here. You may have to do it by hand, or with some other method.

First, let's suppose we have a very simple frequency dependent circuit consisting of a LR voltage divider, with a sine wave source driving the input:

LR filt.png


Using phasor analysis, we could obtain an expression for the output (I should have labeled the output; it's the right two terminals) using the voltage divider rule. We get Vout/Vin = R/(R+sL)

Let's use Laplace transforms to get an expression for the time domain output with a simple sine wave voltage of angular frequency ω applied as Vin.

First get an expression for the transform of a simple sine wave:

LT1.png


Now let's get the inverse Laplace transform of our LR circuit output with a sine wave input. A very important point here is that using this method assumes that Vin is zero until time t=0; at t=0, the sine wave is suddenly applied. In the Laplace domain we multiply the transform of the input sine wave times the expression for the output of the circuit and derive the Inverse Laplace transform to get the time domain voltage at Vout:

LT2.png


This consists of a transient part (in red), a decaying exponential, and a steady state part (in black), which is the voltage waveform after the exponential decays to zero.

Let's plot this waveform. I'll arbitrarily pick some values for R, L and ω, and plot the output waveform (in red) starting at t=0 for several cycles of the waveform. The plot also shows the waveform of Vin (in blue) scaled by 1/5 to make it fit the plot nicely:

LT3.png


You can see the effect of the initial transient (the decaying exponential) at the beginning. Now let's eliminate the exponential part of the time domain expression and plot it again:

LT4.png


Now we have only the steady state part of the output waveform. This shows that the output is just a sine wave phase shifted with respect to the input.

In the next post, I'll show how the phasor method of analysis gets the same result.
 
  • #23
Now let's use the phasor method to get the output voltage waveform of the circuit.

The output voltage is given by Vout = [tex] Vin \frac {R}{R+sL} [/tex]

To get a time waveform we substitute s = jω. Mathematica uses a special symbol for the imaginary unit j; it should be obvious in what follows.

The phasor result is a sine wave if the input is a sine wave, which is the basic assumption of phasor analysis. The magnitude of the output sine wave is given by the magnitude of our (complex arithmetic) expression for the output fraction: [tex] \frac {R}{R+j ω L} [/tex]

The magnitude is given by the square root of the sum of the real part squared and the imaginary part squared, and the angle is the Arctan of the imaginary part divided by the real part. So we would need to separate the real and imaginary parts. Mathematica has a function to do this, and it's relatively simple for this simple circuit. For your transformer it will be much more complicated. Herewith the separation, with the imaginary part in red:

LT5.png


Now we calculate the magnitude and angle of our output sine wave:

LT6.png


We can plot the scaled input sine wave, and the output sine wave using those values:

LT7.png


Here for comparison purposes is the plot of the steady state time waveform from the previous post:

LT4.png


It's identical. Notice how that even for this very simple circuit, the time domain expression derived with a Laplace transform was moderately complicated.

The expression for your transformer is going to be immensely complicated if you derive it via Laplace transform. Using the magnitude and angle expression derived from the phasor analysis I gave in post #8 will be much easier and less complicated looking.

The result you got in post #1 seems fairly simple, but you have a variable, (script) R, involving flux in the core and flux linkages between primary and secondary. This hides a lot of complication; you don't need to involve flux anyway. Using mutual inductance (M) is the way to go.

But, if you must use the Laplace transform, remember that the exponential part should be eliminated if you want the steady state result.

The result you have in post #18 doesn't look right. The exponential part and steady state part should be added together, not multiplied.
 
  • #24
Correct me if my understanding of this is wrong.

So using this circuit, you determined the output to input ratio as R/(R + sL). Now since, this is Vo(s)/Vi(s), you wanted to obtain the function for vo(t), given that vi(t) = sin(wt). So what you basically did was you took the LT of vi(t) so that we will have an explicit function for Vi(s) then you arranged the expression for the ratio of the two s.t. Vo(s) = Vi(s) R/(R + sL)
Then you took the inverse laplace for this, which sounds like convoluting sin(wt) * L^(-1){R/(R + sL)}. The result is the sum of a decaying exp function and another nondecaying function. As t tends to infinity, obviously the decaying exp function approaches 0 and the nondecaying part is the vo(t) in steady state.

If that's the case, then my intuition tells me that my previous solution, excluding vo sinwt, needs to be convoluted with vo sinwt, right? Since in the first place, I took the ILT of the right hand side of I2(s)/V1(s) which is the expression on the paper excluding vo sin wt. And I just mistakenly multiplied it by vo sin wt since I have no prior idea on convolution theorem. But just a few hours ago, I was able to learn it.
 
Last edited:
  • #25
ZenSerpent said:
Correct me if my understanding of this is wrong.

So using this circuit, you determined the output to input ratio as R/(R + sL). Now since, this is Vo(s)/Vi(s), you wanted to obtain the function for vo(t), given that vi(t) = sin(wt). So what you basically did was you took the LT of vi(t) so that we will have an explicit function for Vi(s) then you arranged the expression for the ratio of the two s.t. Vo(s) = Vi(s) R/(R + sL)
Then you took the inverse laplace for this, which sounds like convoluting sin(wt) * L^(-1){R/(R + sL)}. The result is the sum of a decaying exp function and another nondecaying function. As t tends to infinity, obviously the decaying exp function approaches 0 and the nondecaying part is the vo(t) in steady state.

If that's the case, then my intuition tells me that my previous solution, excluding vo sinwt, needs to be convoluted with vo sinwt, right?

Don't say "convoluted"; say "convolved". :smile:

Since I don't how you derived your previous solution, which I assume involved finding Inverse Laplace transforms, I can't answer your question.

You correctly described what I did. You need to do that with the phasor expression for I2/V1 I gave in post #8.
 
  • #26
As you obviously know, in the time domain what you need to do is convolve the function sin[ωt] with the Inverse Laplace transform of the ratio I2/V1. But it's much easier to do in the Laplace domain where multiplication replaces convolution. So your big problem is to find the Inverse Laplace transform of the product of the transform of the input sine wave and the transform of the ratio I2/V1. In other words, you need to find this:

LT9.png


I wouldn't even think of trying to do this without the aid of modern mathematical software; but then I'm spoiled.

Just to give a taste of what your result is going to look like, here's what Mathematica gives for the Inverse transform of just the ratio I2/V1.

LT8.png
 
  • #27
I assume you are a university student. Find out if your institution has network access to a modern mathematical software such as Mathematica, Maple, Matlab, etc. Such a software should enable you to derive inverse Laplace transforms.
 
  • #28
ZenSerpent said:
Sir, also noticed that the answer is not in Amperes.
You should avoid the use of the laplace transform altogether. That also precludes convolution. Instead, either use phasors as I described earlier, or, since you're a math major not an engineering one, solve the equations classically.

The powerful laplace transform enables transient as well as steady-state solutions but this is of no interest here.
 
  • #29
Oh my! So the best option is phasor analysis. Using that on z = I2(s)/V1(s) the time domain function is i2(t) = |z| sin(wt - arg(z)) right?
 
  • #30
ZenSerpent said:
Oh my! So the best option is phasor analysis. Using that on z = I2(s)/V1(s) the time domain function is i2(t) = |z| sin(wt - arg(z)) right?

I explained this in post #23
 
  • #31
rude man said:
You should avoid the use of the laplace transform altogether. That also precludes convolution. Instead, either use phasors as I described earlier, or, since you're a math major not an engineering one, solve the equations classically.

The powerful laplace transform enables transient as well as steady-state solutions but this is of no interest here.

Did you not read the posts following #19?
 
  • #32
Sir rude man, yup, failure to perform convolution is a serious mistake. But if I were to perform convolution, I'll get an expression as hairy as the one posted by The Electrician in the post above. So, I think phasor analysis is the way to go. And I now gained some good insight just now. And I noticed that the intuition is much similar to the concepts discussed in complex number analysis. Now everything appears to be clear to me.
 
  • #33
The Electrician, so the expression I mentioned in #29 is correct right? One thing I noticed is that all the units cancel out. Why is this?
 
  • #34
ZenSerpent said:
The Electrician, so the expression I mentioned in #29 is correct right? One thing I noticed is that all the units cancel out. Why is this?

sin(ω t) has units of volts. That's the units of your final answer.
 
  • #35
The Electrician said:
I explained this in post #23
Yes, but don't say "I(s), V(s) etc. Avoid "s" completely. Say I(jw), V(jw) etc. which are phasors.
 

Similar threads

  • Introductory Physics Homework Help
Replies
6
Views
266
  • Introductory Physics Homework Help
Replies
10
Views
302
  • Introductory Physics Homework Help
Replies
2
Views
27
  • Introductory Physics Homework Help
Replies
4
Views
250
  • Introductory Physics Homework Help
Replies
2
Views
59
  • Introductory Physics Homework Help
Replies
6
Views
776
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
3
Views
1K
  • Advanced Physics Homework Help
Replies
1
Views
938
Replies
59
Views
6K
Back
Top