Trouble with use of Symmetrical components

  • Thread starter I_am_learning
  • Start date
  • Tags
    Components
In summary: Ib2;etc.I fully agree that mathematic ally, 3 phase unbalanced set of currents (or any phasors) can be thought off as sum of 3 sequence components.What I disagree is when people talk about the effects of these currents. For example I don't think we can say the losses in stator winding = (I_positive^2*r + I_negative^2*r + I_zero^2*r).Mostly, I find texts talking about negative sequence currents."Since negative sequence currents produce rotating magnetic fields in opposite direction, it will have large relative velocity with rotor (nearly 2*Ns , Ns is synchronous speed
  • #1
I_am_learning
682
16
I see some trouble with how symmetrical components are treated. In lots of texts, I have heard something along these lines
When the current in a 3 phase motor is unbalanced, we can resolve it into three sets of balanced currents.
1. Positive sequence currents.
These produce rotating magnetic fields in usual direction and produces +ve torque and power
2. Negative sequence currents
There produce rotating magnetic fields in opposite direction and produce -ve torque
3. Zero sequence currents
These produce stationary and pulsating magnetic fields and produce no torque.

Fine upto now. the net torque is sum of all torques.
I fully agree that mathematic ally, 3 phase unbalanced set of currents (or any phasors) can be thought off as sum of 3 sequence components.

What I disagree is when people talk about the effects of these currents.
For example I don't think we can say the losses in stator winding = (I_positive^2*r + I_negative^2*r + I_zero^2*r).
Mostly, I find texts talking about negative sequence currents.
"Since negative sequence currents produce rotating magnetic fields in opposite direction, it will have large relative velocity with rotor (nearly 2*Ns , Ns is synchronous speed). It will create large induced currents in rotor and huge eddy losses."
But I don't think we are allowed to find out the induced currents and eddy losses due to the 3 sequence currents individually, just like we can't find the I^2*R losses individually.

For example, consider that a DC current of 2A is flowing in one of the winding of a motor. Or even better, let's consider a motor with no current in any winding.
We can think of 0 current as 0 = 100*Sin(wt) + (-100*Sin(wt)) , as composed of two AC currents. Now Clearly, we can't individually calculate the losses (eddy and I^2*R) due to each current and Add.

Please help me learn. :)
 
Last edited:
Engineering news on Phys.org
  • #2
i've heard of Fortescue's theorem, but never studied it. I heard of sequence analysis from some genuine power engineers who were in relay department at same plant i worked.. So i am very foggy on it.

But - aren't you just saying the sum of the squares doesn't equal the square of the sum?

Near the end of this link, a kindly professor speaks to power associated with sequence components. Each sequence gets its power calculated independently and they are summed.

http://www.elect.mrt.ac.lk/EE201_3phase_sym_comp.pdf

Thus P = 3 (Va0 Ia0 cos φ0 + Va1 Ia1 cos φ1 + Va2 cos φ2)


I hope to learn along with you on this one.

old jim
 
  • #3
I_am_learning said:
... I don't think we are allowed to find out the induced currents and eddy losses due to the 3 sequence currents individually, just like we can't find the I^2*R losses individually.

From the Wikipedia page Fault (power engineering) (bold by me),

To determine the currents resulting from an asymmetrical fault, one must first know the per-unit zero-, positive-, and negative-sequence impedances of the transmission lines, generators, and transformers involved. Three separate circuits are then constructed using these impedances. The individual circuits are then connected together in a particular arrangement that depends upon the type of fault being studied (this can be found in most power systems textbooks). Once the sequence circuits are properly connected, the network can then be analyzed using classical circuit analysis techniques. The solution results in voltages and currents that exist as symmetrical components; these must be transformed back into phase values by using the A matrix.

where the A matrix is

406b237b685dce3e9132d7e6b56470ac.png


from the Wikipedia page Symmetrical components.
 
Last edited:
  • #4
The impedance of a synchronous generator for each sequence can be measured or calculated. And they are not always equal to stator and rotor resistance and Xd, Xq etc. So in your first example, the stator resistance might not be; r=r0=r1=r2. And hence the equation is wrong.

The transformation is power invariant, so power calculated in abc sequence should equal the 012 sequence. Thus using the correct measured or calculated resistance for each sequence should give the same answer as using normal quantities.

Disclaimer: This is just my quick reasoning, so I could be wrong.
 
  • #5
jim hardy said:
i've heard of Fortescue's theorem, but never studied it. I heard of sequence analysis from some genuine power engineers who were in relay department at same plant i worked.. So i am very foggy on it.

But - aren't you just saying the sum of the squares doesn't equal the square of the sum?

Near the end of this link, a kindly professor speaks to power associated with sequence components. Each sequence gets its power calculated independently and they are summed.

http://www.elect.mrt.ac.lk/EE201_3phase_sym_comp.pdf


I hope to learn along with you on this one.

old jim
After litter more pondering today, I think I found the answer.
Here is what I got.
Resolving a set of 3 phase unbalanced currents into sequence components is purely a mathematical thing.
You have right to say
Ia = Ia0 + Ia1 + Ia2;
Ib = Ib0 + Ib1 + Ib2;
Ic = Ic0 + Ic1 + Ic2;
where Ia1, Ib1 and Ic1 form +ve sequnce balanced set (i.e. phase sequence of abc) whereas Ia2, Ib2 and Ic2 form -ve sequence balanced set (i.e phase sequence of acb)
Ia0, Ib0 and Ic0 form zero sequence. (all thre currents are in phase)
The problem is just finding correct magnitude for |Ia0|, |Ia1| and |Ia2|. But mathematics has the answer.

Now when unbalanced current Ia, Ib and Ic is flowing in motor, you can substitute Ia, Ib and Ic with their respective sums of sequence components.
The actual loss in winding is Ia^2*r = (Ia0 + Ia1 + Ia2)^2*r
So, its not equal to Ia0^2*r + Ia1^2*r + Ia2^2*r.
Simple and easy.
The magnetic field produced is Ia*K = (Ia0+Ia1+Ia2)*K = Ia0*K + Ia1*K + Ia2*K
where K is some constant.

So it is evident that, if the feature being calculated is proportional to I^2 then we can't calculate it separately with different sequence components and add(The former case i.e I^2*r case)

But if its is proportional to just I, then we can calculate the quantity separately for 3 sequence components and then Add. (the second case, i.e. Magnetic field case)

So, we can say that The magnetic fields, The torque produced, The voltage induced in rotor, the current induced in rotor, all can be calculated separately and then added.
However the power induced (lost) in rotor (or stator) can't be separately calculated and added.

So, yes jim, it basically boils down to "sum of the squares doesn't equal the square of the sum".

But texts sometimes seem to miss this point. Its true that negative sequence currents in stator windings create large induced currents in the rotor.
But it would be wrong to say this large induced current will create large loss in rotor.
Because, before finding the losses due to induced current by -ve sequence currents in stator, we need to find induced current by +ve and 0 sequence currents in stator and add all three induced currents. I_total = I_induced_-ve + I_induced_+ve + I_induced_0
The loss will then be I_total^2*r.

So, although I_induced_-ve might be large, it might be canceled or reduced by I_induced_+ve and/or I_induced_0

But I don't see that being mentioned in texts. See for eg. in this document. Page 13
http://www.basler.com/downloads/negseqcurrent.pdf
The current induced at the rotor center is of double frequency. The induced current could cause rapid
heating in the rotor, which may result in insulation failure and/or mechanical problems.

Although in the case analyzed in the document, I_induced_+ve and I_induced_0 is actually 0 and I_total is indeed I_induced_-ve alone; its generally wrong to jump to rotor heating or other power losses conclusion based on induced current by only one sequence components.

Even on other texts, where I_induced_+ve isn't 0 (induction motors) I see similar conclusions being made. And that was the reason for starting this thread in the first place.

I_induced_0 is always 0 in an electric machine because zero sequence current don't produce any net magnetic fields.
Correcting my OP
3. Zero sequence
The magnetic field produced by 3 coils carrying Zero sequence currents cancel each other and produce no net magnetic field.

Thanks for showing interest.
 
Last edited:
  • #6
i have thought aboout this... am away from home so no books handy

but you're right math has the answer.

i finally realized your currents are complex
so when you square them you CAN get a negative result, unlike squaring a real number.

Square (1 +j 3) and see what you get
1 +j6 - 9 ?

so powers might very well sum to zero ?
 
  • #7
I_am_learning said:
1. Positive sequence currents.
These produce rotating magnetic fields in usual direction and produces +ve torque and power
2. Negative sequence currents
There produce rotating magnetic fields in opposite direction and produce -ve torque

BEWARE that the rotor has only single direction of rotation for these two current rotations!

Then, the reversed current rotation produces a braking torque, but not of the same strength as the normal moment! In a squirrel cage motor, the braking torque would be much smaller because of the high slip, which induces high frequency in the rotor, whose inductance limits the induced current. Similar to the small starting couple but worse.
 

Related to Trouble with use of Symmetrical components

What is the concept of Symmetrical components?

The concept of Symmetrical components is a mathematical technique used in power system analysis to simplify complex three-phase systems into simpler single-phase systems. This method is based on the principle that any three-phase system can be represented by three symmetrical single-phase systems.

Why is the use of Symmetrical components important in power system analysis?

The use of Symmetrical components is important in power system analysis because it simplifies the analysis of unbalanced three-phase systems. It allows for easier calculation of fault currents and voltages, as well as the identification of fault locations in the system.

What are the applications of Symmetrical components in power systems?

The applications of Symmetrical components in power systems include fault analysis, protective relaying, and power flow analysis. This technique is also used in the design and operation of power system protection schemes.

What are the limitations of Symmetrical components?

One of the limitations of Symmetrical components is that it assumes the three-phase system is perfectly balanced. In reality, most three-phase systems are unbalanced to some extent. This can lead to inaccurate results when using Symmetrical components for analysis.

How can the use of Symmetrical components be improved?

To improve the use of Symmetrical components, advanced techniques such as sequence impedance and sequence networks can be used. These techniques take into account the unbalanced nature of three-phase systems and provide more accurate results for power system analysis.

Similar threads

  • Electrical Engineering
Replies
18
Views
2K
  • Electrical Engineering
Replies
3
Views
853
Replies
14
Views
3K
  • Electrical Engineering
Replies
7
Views
3K
Replies
10
Views
1K
  • Electrical Engineering
Replies
5
Views
2K
Replies
8
Views
808
Replies
5
Views
4K
  • Electrical Engineering
Replies
1
Views
2K
Replies
3
Views
663
Back
Top