Synchronous Motor Capacitor Sizing

In summary, the capacitor appears to be there to smooth DC field current after it is rectified. It is likely for this purpose that it is a large capacitor, as this would provide the smoothest DC current. The capacitor may have blown up due to arcing, which is a problem due to the high voltages that can be generated. An event may have caused the machine to produce high voltage, in which case the capacitor may have been necessary to protect the machine. A temporary light bulb may be enough to check for this problem. If the machine does not illuminate with full exciter voltage, there may be a problem with the field.
  • #1
JeffryCampbell
4
0
I am troubleshooting a 1967 GE synchronous motor used to run a reciprocating compressor. It is a 1000 HP machine. I am trying to figure out the size and purpose of the capacitor connected to the DC field. Is it there to absorb voltage fluctuations?

The capacitor has burnt up and can't be tested (arcing destroyed it)

Nameplate data:
KVA 800 Horsepower 1000 Volts 2300 Amp 200 RPM 225 cycles 60 Phase 3 PF 1.0
Excitation Volts 250 Amp 79
 

Attachments

  • nameplate 31.jpg
    nameplate 31.jpg
    44.9 KB · Views: 5,695
Engineering news on Phys.org
  • #2
Capacitor across the field? I'd have expected either a "field discharge resistor" or a surge arrestor.


https://www.gedigitalenergy.com/products/manuals/spm/spmman-a9.pdf
Shunting a resistor around the motor field during starting is accomplished with a field contactor. Optimum application of excitation (that is, closing the field contactor) requires accurate sensing of motor speed and rotor angle. This SPM provides this function. Optimum speed for pull-in varies with motor design and with the field discharge resistor value

Can you post a photo of the capacitor ? Blowing up such parts suggests the amortisseur windings could need attention.

See also this presentation, page 29:
http://www.wmea.net/Technical%20Papers/May-2009-Sync-Motor-Excitation-a.pdf
Open circuit fields during start creates high voltages [10,000 volts or more] – damage to fields, slip rings!
Either a short circuit or a resistor should be used during start.
Using an optimal resistor can give 30-50% more start torque

“Thyrite” voltage surge protectors act as backup to resistors and contactors across the fields

good luck !

old jim
 
  • #3
The field current is probably rectified from an AC source. The capacitor is probably for smoothing the DC field current after it is rectified. These are just guesses based on other applications I've seen. More information would help.

What excites the field? Are there any other big Caps in that circuit?
 
  • #4
The capacitor is probably for smoothing the DC field current after it is rectified.

I've wracked my brain and cannot figure out why anybody would put a capacitor of any size across the inductive field of a synchronous machine. It opens the door to subsynchronous resonance troubles.

I hope we see a picture of the gizmo. I'd expect a selenium surge suppressor.
http://www.deantechnology.com/pg_common/DisplPDF.aspx?ItemIndex=13&DbTable=techinfo
 
Last edited by a moderator:
  • #5
jim hardy said:
I've wracked my brain and cannot figure out why anybody would put a capacitor of any size across the inductive field of a synchronous machine.

I think you are correct and now I can't remember what I had in mind...
 
  • #6
More Investigation

I may have been leading you in the wrong direction(as i was), it appears to be a shaft grounding system. The brush being directly on the shaft before the compressor, connected to the resistor?, then to ground through the motor casing.

I think I'm looking for resistor sizing, thanks for any help.
 

Attachments

  • Brush on shaft.jpg
    Brush on shaft.jpg
    20.7 KB · Views: 666
  • brush assembly.jpg
    brush assembly.jpg
    30.9 KB · Views: 694
  • IMG_20140915_152603.jpg
    IMG_20140915_152603.jpg
    19.5 KB · Views: 635
  • #7
Here's an educational article on shaft grounding.
http://www.marubun.co.jp/product/measurement/electric/qgc18e000002i83w-att/nip_understanding_803.pdf

Shaft voltage is normally modest, the grounding brush is basically just a static drain.

Why'd it blow?
Was there some sort of event on this machine?
Centrifugal shorts are really hard to find because they go away when the machine slows down.

I'd replace it temporarily with a 240 volt light bulb , around 200 watts . If it illuminates there's trouble enough that it should be easy to find. There should be not more than a very few volts on the shaft when it's connected through such a low impedance. But the lamp won't explode if it sees full exciter voltage.(unless the field breaker trips).

Meantime maybe somebody will find the instruction book for that device. Could it be a capacitor to suppress RF from brush arcing?

Are both bearing housings insulated or just one?
 
Last edited by a moderator:
  • #8
The brush assembly was not being maintained properly and there was some major arcing. This is the only brush directly on the shaft. I like the light bulb idea!
 
  • #9
' major arcing' ?

Shaft voltage arises from magnetic imbalance in the machine. Flux that's asymmetric around the shaft couples it so current tries to circulate along shaft , through bearings and back via motor frame.
A couple volts is typical open circuit . If neither bearing is insulated a very few amps might flow depending on imbalance.

Above around 500 horsepower machines are big enough it's necessary to insulate one bearing to break the circuit. Shaft current will pit journal bearings. It makes ball bearings acquire stripes so regular that your first impression is "What in the world put those raccoon tail stripes on that bearing race ? " Of course when the bearing fails catastrophically it wipes out the evidence. The natural reaction then is to mutter "Galling" and try a different grease.

When VFD's became commonplace , shaft current troubles moved into the world of small motors. So there's a LOT of information out there now much of it scholarly. Thirty five years ago it was mysterious.. i wracked my [edit:[STRIKE]brain[/STRIKE] ]alleged brain over a pair of 450KVA machines that intermittently ate bearings. They weren't insulated..

If you have significant arcing it suggests to me you might have trouble beyond a dirty brush. Maybe the insulated bearing is no longer insulated ?
Is something elevating that shaft voltage well above ground ?
It's worth looking at some simple things . Light bulb tells you something even if it stays dark.

How's the vibration on that machine? Does it vary with excitation? That'd be a symptom of shorted rotor turns which cause magnetic imbalance - you have less mmf hence less flux at slots with a shorted turn. Those can be centrifugal and if bad enough can ground the field...
These guys' Dad literally 'wrote the book' on diagnosing shorted rotor turns in-situ.
Red trace is slot by slot mmf.

http://www.generatortech.com/
Analysis%20Graph%20square%20a.jpg


Good luck - keep us posted !

old jim
 
Last edited:
  • #10
Hmmm, peel it open and let's see what's inside!
 
  • #11
It is a capacitor, we were finally able to shut down a similar machine and it tested and 6.8 uf. We cleaned up the leads on the "bad" one and it tested the same.

Question is, why a capacitor to ground on a shaft grounding system?
 
  • #12
JeffryCampbell said:
It is a capacitor, we were finally able to shut down a similar machine and it tested and 6.8 uf. We cleaned up the leads on the "bad" one and it tested the same.

Question is, why a capacitor to ground on a shaft grounding system?


my GUESS is it's a high frequency bypass to keep RF caused by sparking at the grounding brush from propagating on down the wires to whatever (if any) shaft voltage monitoring system is there.

You see a similar application on old brush style car generators. It keeps brush static out of the radio.
Day3-teardown-010-S.jpg


An old fashioned pocket transistor radio is useful for keeping an eye on big motors. Set it to AM and tune between stations. Walk around the motor listening to the radio. You'll get used to how radio-noisy it is . A change is an early warning that you are developing arcing or corona . Try it on rainy vs dry days... search on "Partial Discharge Monitoring"

old jim
 

Related to Synchronous Motor Capacitor Sizing

What is a synchronous motor capacitor?

A synchronous motor capacitor is an electrical component that is used to improve the power factor and efficiency of a synchronous motor. It is connected in parallel with the motor and helps to reduce the reactive power of the motor, which in turn reduces the overall power consumption.

Why is capacitor sizing important for synchronous motors?

Capacitor sizing is important for synchronous motors because it ensures that the motor is operating at its optimal power factor. This not only improves the efficiency of the motor, but also reduces the strain on the motor and other connected equipment. Additionally, proper capacitor sizing can also help to avoid penalties for low power factor from utility companies.

How do you determine the correct size of a capacitor for a synchronous motor?

The correct size of a capacitor for a synchronous motor is determined by calculating the reactive power of the motor and then selecting a capacitor that can provide the necessary reactive power to bring the power factor to the desired level. This calculation takes into account the motor's voltage, current, and power factor.

What are the consequences of using an incorrectly sized capacitor for a synchronous motor?

Using an incorrectly sized capacitor for a synchronous motor can cause several issues. If the capacitor is too small, it may not be able to provide enough reactive power, resulting in a low power factor and reduced efficiency. On the other hand, if the capacitor is too large, it can cause overcompensation and lead to an overvoltage condition, which can damage the motor and other connected equipment.

How often should synchronous motor capacitors be checked and replaced?

Synchronous motor capacitors should be checked and replaced periodically to ensure they are functioning properly. The frequency of replacement depends on the operating conditions and the type of capacitor being used. Generally, it is recommended to check and replace capacitors every 5-7 years to maintain optimal performance.

Similar threads

  • Electrical Engineering
Replies
2
Views
2K
  • Electrical Engineering
2
Replies
45
Views
14K
  • Electrical Engineering
Replies
4
Views
16K
  • Introductory Physics Homework Help
Replies
20
Views
33K
  • General Engineering
Replies
18
Views
34K
Back
Top