Smoothing DC Output from Transformer

In summary: Ideally you'd have a scope to measure the ripple reduction, but functional testing would work well too. See if you get more stable readings. Check your output voltage is within limits. If all goes well, buy a decent low ESR cap and find a way to fit it neatly into the supply enclosure.
  • #1
JaredJames
2,818
22
I have a power supply which takes 230 VAC input and gives 24 VDC output. I use it to drive some differential pressure sensors (24 VDC supply and 0-10 VDC signal output).

It is stated to have a noise of 80 mV peak to peak. This can equate to a 25 Pa variation in readings

I'm finding with certain instruments they can jump around a fair bit and I suspect the ripple is the cause.

Is it worth me trying to further smooth this in some manner, such as by putting a capacitor parallel to the load? I'm not sure if it will provide any useful reduction in the noise and don't want to tear the device apart without some confidence.

For reference, I also have a low noise supply with 1 mV peak to peak, where the readings stay stable to within 1 Pa. Hence my suspicion that it's due to the noise.

The only alternative is that it's some smoothing done within the software that I'm not aware of on the original device, that I haven't added to my own.

Any help / ideas appreciated.
 
Engineering news on Phys.org
  • #2
JaredJames said:
I have a power supply which takes 230 VAC input and gives 24 VDC output. I use it to drive some differential pressure sensors (24 VDC supply and 0-10 VDC signal output).

is this a commercial one or one you have built ?

JaredJames said:
Is it worth me trying to further smooth this in some manner, such as by putting a capacitor parallel to the load? I'm not sure if it will provide any useful reduction in the noise and don't want to tear the device apart without some confidence.

the answer to this in some part depends on the answer to my first Q

But additional smoothing capacitors isn't an issue ... what sort of current is your circuit ( all of it) drawing ?

Dave
 
  • #3
JaredJames said:
For reference, I also have a low noise supply with 1 mV peak to peak, where the readings stay stable to within 1 Pa. Hence my suspicion that it's due to the noise.
If the voltage levels can work out, one common way to fix this is to follow your transformer, full-wave rectifier and smoothing caps with a low dropout linear voltage regulator. You need the minimum voltage input to the regulator (the troughs of the input ripple voltage) to stay above the dropout voltage of the linear regulator (hence why you use a low dropout regulator). If the troughs of the input voltage across the capacitors at full output current loading is 23.5V, you could probably manage about a 22.5V output voltage from your adjustable low dropout linear voltage regulator, and it should be nice and quiet.

http://www.williamson-labs.com/images/pwr-supply-vr-linear-446.gif
pwr-supply-vr-linear-446.gif
 
  • #4
Thanks for the responses.

davenn said:
is this a commercial one or one you have built ?

This is a commercially bought one.

This one to be exact: http://uk.rs-online.com/web/p/din-rail-panel-mount-power-supplies/0428445/

Looks like the noise is 150 mV peak to peak (previously said 80 mV).

davenn said:
what sort of current is your circuit ( all of it) drawing ?Dave

The sensor draw is tiny. Only a few mA.
 
  • #5
berkeman said:
If the voltage levels can work out, one common way to fix this is to follow your transformer, full-wave rectifier and smoothing caps with a low dropout linear voltage regulator. You need the minimum voltage input to the regulator (the troughs of the input ripple voltage) to stay above the dropout voltage of the linear regulator (hence why you use a low dropout regulator). If the troughs of the input voltage across the capacitors at full output current loading is 23.5V, you could probably manage about a 22.5V output voltage from your adjustable low dropout linear voltage regulator, and it should be nice and quiet.

Thanks for the reply.

So would we be looking at a lower output voltage than 24V if I implemented smoothing? I may get away with a small drop, but a couple of volts may not be feasible.
 
  • #6
JaredJames said:
Thanks for the reply.

So would we be looking at a lower output voltage than 24V if I implemented smoothing? I may get away with a small drop, but a couple of volts may not be feasible.
My (fairly crude) approach would be to pull a cap, say 50V rated, the larger capacitance the better, from a scrap board (do you have a box of scrap boards? You should!) and rig it across the 24V output with some jumpers.

Ideally you'd have a scope to measure the ripple reduction, but functional testing would work well too. See if you get more stable readings. Check your output voltage is within limits.

If all goes well, buy a decent low ESR cap and find a way to fit it neatly into the supply enclosure.

I had a similar problem with an 12V electric fence energiser that refused to run from a ripply battery charger supply. A CRC filter, two parallel caps with a series power resistor inbetween, had a dramatic effect on the ripple, and the current draw was low so the resistor hardly dissipated any heat.
 
  • #7
JaredJames said:
Thanks for the responses.
This is a commercially bought one.

This one to be exact: http://uk.rs-online.com/web/p/din-rail-panel-mount-power-supplies/0428445/

Looks like the noise is 150 mV peak to peak (previously said 80 mV).[/QUOTE

ok :smile:
The sensor draw is tiny. Only a few mA.

I did ask for ALL of it, not just the sensor
davenn said:
what sort of current is your circuit ( all of it) drawing ?

and speaking of ALL the circuit, it's probably way past time you showed us ALL of it, specially after comments like this ...

JaredJames said:
So would we be looking at a lower output voltage than 24V if I implemented smoothing? I may get away with a small drop, but a couple of volts may not be feasible.

If we knew what your circuit looked like, type of sensor etc ... better suggestions could be made to help youDave
 
  • #8
  • #9
JaredJames said:
Your sketch shows 24V shorted to GND in two places...
JaredJames said:
So would we be looking at a lower output voltage than 24V if I implemented smoothing? I may get away with a small drop, but a couple of volts may not be feasible.
That's why you use a low dropout linear regulator -- to minimize the voltage drop. You should be able to get away with about 0.5V drop at your low currents, but check the datasheet for whatever part you choose to see what the dropout voltage is.
JaredJames said:
That looks like a switching power supply, not a line frequency transformer with rectifier and capacitive output filter. What frequency is the ripple voltage? Probably a few 100kHz? Be careful just adding capacitance to the output of a switching power supply -- there could be stability issues. Check the power supply datasheet to see if it specifies a maximum output capacitance...
 
  • #10
That IS a switching power supply. The ripple is 150mV p-p, as you say, but is this not a maximum? Under low current draw, I suspect it'll be a lot less. Is the voltmeter/sensor really being affected by kHz range ripple?

Perhaps a better solution would be a 0-30V supply, put through a linear regulator as suggested.
 
  • Like
Likes berkeman
  • #11
Switching power supplies are inherently noisy. They make RFI at switching frequency that shows up as 'ripple' .
For your light load you might look for a "Wall Wart" transformer based linear supply. Linears are electrically much more quiet.
they look like this
upload_2017-8-24_11-57-31.png


A Linear weighs about three times as much as a Switcher, so they're easy to distinguish
Rating is always printed on the case. .
Most thrift shops have a basket full of them for around $1 .. Get a couple heavy ones and see what they do ?
Some are regulated some are not. An unregulated 24V one will likely put out 27 volts or so at light load.

It's not impossible to build a 'quiet' switcher, just difficult to do it cheap enough for the consumer market.

Good luck with your project.

Have you a a link to your pressure sensor's datasheet ? Could be some filtering on its output would solve your trouble.

old jim
 
  • #12
jim hardy said:
It's not impossible to build a 'quiet' switcher

How would a money-no-object, quiet switching supply be made? Or is this a subject for another thread?
 
  • #13
Guineafowl said:
How would a money-no-object, quiet switching supply be made? Or is this a subject for another thread?
Generally you follow the switcher with a linear regulator (usually an LDO regulator). That's what we often do for RF transceivers that can get desensitized by a noisy power supply.
 
  • Like
Likes Guineafowl
  • #14
Filters on all wires entering and exiting and lots of RF shielding.

Then you put it in an RF emissions test rig and measure what RF leaks out, keep fixing leaks until it meets your standard..
Here's an outfit offering that service
http://www.curtisind.com/files/pdf/RFI-Filters-Conducted-Emissions-Testing.pdf

Take apart some laptop power supplies. You'll probably find better ones have copper foil RF shielding inside.

I'd just stick with a linear supply.
 
  • Like
Likes dlgoff and Guineafowl
  • #15
Thanks all for the information. Didn't realize there was a difference between the supplies (switching / linear - I'm not electrical).

jim hardy said:
I'd just stick with a linear supply.

I bought a fairly cheap 24 VDC supply as suggested and tried it. Worked very well. The fluctuation in values is a lot lower.

I also tried the low noise supply that was available (the device was now in pieces so figured why not) and it was even better.

Reading the comments here, it's surprising that I would register such noise on a voltmeter.
 
  • #16
If it is just a question of reducing the ripple, this simple circuit does so.

upload_2017-8-27_7-31-34.png
 

Related to Smoothing DC Output from Transformer

1. How does a transformer affect DC output?

A transformer converts high voltage AC power to low voltage DC power. This process can cause fluctuations in the DC output, resulting in an uneven or "spiky" output.

2. What is the purpose of smoothing DC output from a transformer?

The purpose of smoothing DC output is to remove any fluctuations or ripples in the output, providing a more stable and consistent supply of power. This is important for electronic devices that require a steady source of power to function properly.

3. How can I smooth the DC output from a transformer?

There are several methods for smoothing DC output from a transformer, including using a capacitor, inductor, or voltage regulator. These components can filter out the ripples and provide a more constant output.

4. What are the potential consequences of not smoothing DC output from a transformer?

If the DC output is not smoothed, it can cause damage to electronic devices that are sensitive to fluctuations in power. It can also result in inaccurate readings or incorrect functioning of the device.

5. Is there a way to test the effectiveness of smoothing on DC output?

Yes, there are tools such as an oscilloscope that can measure the ripples in the DC output and show the effectiveness of smoothing. Additionally, testing the device with and without smoothing can also demonstrate the impact on performance.

Similar threads

  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
10
Views
2K
  • Electrical Engineering
2
Replies
63
Views
5K
  • Electrical Engineering
Replies
12
Views
2K
  • Electrical Engineering
Replies
18
Views
2K
  • Electrical Engineering
Replies
9
Views
3K
Replies
6
Views
2K
  • Electrical Engineering
Replies
1
Views
999
Replies
3
Views
2K
  • Electrical Engineering
Replies
3
Views
1K
Back
Top