Required water pressure to find air leak

In summary: I've ever heard of --- as in not broken, don't fix it. If it's something else, instrument air, or whatever, and has to be tight, check the "hard" plumbing separately from any soft/flexible lines.In summary, to check for an air leak at 130 psi of air, you would need to put water pressure on the system and calculate the viscosity and surface tension of water and air.
  • #1
Tileguy
5
0
I have an air leak somewhere in a coil or 20 feet of pipe in a mechanical room next to a transformer. I have 160 psi of air on the system and it dropped 30 psi in two days.

I have tried to find the lead with 60 psi of water currently but no success. I do not want to put a lot of water pressure on the system and have the leak show itself in a marvelous fashion and ruin the transformer.

My question is: How can I calculate how much water pressure is needed to identify the air leak at 130 psi of air?

I know the viscosity information and the surface tension for water and the viscosity for air but I have no idea on how to apply them to an equation. I have zero success finding anything online about this, so any help would be greatly appreciated.
Thank you.
 
Physics news on Phys.org
  • #2
Coil of what? Rubberized air line? What's the volume of the line and pipe? If this is "utility" air for driving pneumatic tools, you've got the tightest system I've ever heard of --- as in not broken, don't fix it. If it's something else, instrument air, or whatever, and has to be tight, check the "hard" plumbing separately from any soft/flexible lines.
 
  • #3
Tileguy said:
I have an air leak somewhere in a coil or 20 feet of pipe in a mechanical room next to a transformer. I have 160 psi of air on the system and it dropped 30 psi in two days.

I have tried to find the lead with 60 psi of water currently but no success. I do not want to put a lot of water pressure on the system and have the leak show itself in a marvelous fashion and ruin the transformer.

My question is: How can I calculate how much water pressure is needed to identify the air leak at 130 psi of air?

I know the viscosity information and the surface tension for water and the viscosity for air but I have no idea on how to apply them to an equation. I have zero success finding anything online about this, so any help would be greatly appreciated.
Thank you.

Larger leaks in gas lines can be checked with "Snoop" (basically soapy water). Smaller leaks can be found with a He leak detector -- overpressure the system with He, and scan the outside with a probe. Some other kinds of commercial gas detectors can be used, as well, in a way similar to the He leak detector. If you are near a physics department, they may have a He leak detector for detection of leaks in vacuum equipment.
 
  • #4
It's a copper coil for warming air that is going through a Air Handler Unit. I'm currently testing it with air to verify there are no leaks. Water will be flowing through it in the future to heat the air that passes through the coil. There are zero flexible lines in this system, it is all hard copper piping.

I just want to figure out how to determine what pressure of water I would need to identify the leak I have with 160 psi of air.
 
  • #5
Quantum Defect said:
Larger leaks in gas lines can be checked with "Snoop" (basically soapy water). Smaller leaks can be found with a He leak detector -- overpressure the system with He, and scan the outside with a probe. Some other kinds of commercial gas detectors can be used, as well, in a way similar to the He leak detector. If you are near a physics department, they may have a He leak detector for detection of leaks in vacuum equipment.

I have sprayed everything I can with a micro leak detection fluid already with no success, which leads me to believe that the problem is in the coil which I cannot spray down. I agree with He use but that is not practical where I am located or I would definitely do it.
I would just like to put enough water pressure to it in order to find the leak I have with air. There has to be some sort of mathematical formula to use that can accomplish this.
 
  • #6
Tileguy said:
It's a copper coil for warming air that is going through a Air Handler Unit. I'm currently testing it with air to verify there are no leaks. Water will be flowing through it in the future to heat the air that passes through the coil. There are zero flexible lines in this system, it is all hard copper piping.

I just want to figure out how to determine what pressure of water I would need to identify the leak I have with 160 psi of air.

If the system is going to be filled with water (low pressure) for a heat exchanger, I might not worry about such a small air leak at 160 psi. You won't be running anywhere near that pressure, no? It may not leak under normal operating conditions.

If you are committed to finding any possible water leak, another strategy is to put some very fluorescent water-soluble dye (fluorescein or rhodamine) in water, fill the system, and look for a leak with a uv lamp -- they have these at pet stores for finding cat pee! Or you could fill the system with cat pee... ;)

The only draw back with this method is that your system will be filled with a brightly colored dye that may be difficult to clean out. If the cooling water is closed cycle, then it doesn't really matter.
 
  • #7
Quantum Defect said:
If the system is going to be filled with water (low pressure) for a heat exchanger, I might not worry about such a small air leak at 160 psi. You won't be running anywhere near that pressure, no? It may not leak under normal operating conditions.

If you are committed to finding any possible water leak, another strategy is to put some very fluorescent water-soluble dye (fluorescein or rhodamine) in water, fill the system, and look for a leak with a uv lamp -- they have these at pet stores for finding cat pee! Or you could fill the system with cat pee... ;)

The only draw back with this method is that your system will be filled with a brightly colored dye that may be difficult to clean out. If the cooling water is closed cycle, then it doesn't really matter.

The system will only be around 50 psi of water which I know will not leak, but my foreman has this strict requirement to pass with no leakage at 150 psi of air in this mechanical room. I know that this is rediculous, but I am just doing as I am told.

The dye will not work currently since it is not leaking any water which would be visible and I have to get the pressure of the water higher to counter the higher viscosity and the surface area that it has over air. I just need to know at what pressure water will start to show itself.

With a mathematical formula in hand I can show the foreman that this is the pressure I have to take it to in order to identify the leak. He is very anal about getting water in the transformer and blowing it up. I need to show him that 60 psi of water will not equate to 160 psi of air for leak detection purposes. Any sane person can obviously tell that air will leak through an opening before water will but there is no reasoning with him. I need some cold hard calculations to show him
 
Last edited:
  • #8
Bystander said:
Coil of what? Rubberized air line? What's the volume of the line and pipe? If this is "utility" air for driving pneumatic tools, you've got the tightest system I've ever heard of --- as in not broken, don't fix it. If it's something else, instrument air, or whatever, and has to be tight, check the "hard" plumbing separately from any soft/flexible lines.

As for the volume, I have about 20 gallons worth of piping. I could convert it to cubic feet but gallons works too.
 
  • #9
Tileguy said:
As for the volume, I have about 20 gallons
So, four "gallons" of air loss times twelve atmospheres is 48 gallons of air in two days is around a "gallon" an hour. You could be blowing the "snoop" away from the leak so fast that you won't see bubbles. Cut the pressure and look again.
 
  • #10
Tileguy said:
With a mathematical formula in hand I can show the foreman that this is the pressure I have to take it to in order to identify the leak. He is very anal about getting water in the transformer and blowing it up. I need to show him that 60 psi of water will not equate to 160 psi of air for leak detection purposes. Any sane person can obviously tell that air will leak through an opening before water will but there is no reasoning with him. I need some cold hard calculations to show him

If he is doing his job, he will not accept what you have gotten via the Internet. The liability issues are too great. Thread is closed.
 

Related to Required water pressure to find air leak

1. What is the purpose of finding air leaks?

The purpose of finding air leaks is to prevent energy and cost losses in buildings. Air leaks can cause drafts, decrease indoor air quality, and increase heating and cooling expenses.

2. How is water pressure used to find air leaks?

Water pressure is used to pressurize the building's interior, forcing air to escape through any leaks. By measuring the pressure drop, the location and severity of the air leaks can be determined.

3. What is the required water pressure to find air leaks?

The required water pressure to find air leaks varies depending on the size and complexity of the building. Generally, a pressure of 25-30 Pascals (0.1 inch of water column) is recommended.

4. Can water pressure damage the building during the leak detection process?

It is important to use caution when applying water pressure to a building. High water pressure can potentially damage weak or vulnerable areas, so it is crucial to use appropriate equipment and techniques to avoid causing harm.

5. Are there any alternative methods for finding air leaks besides using water pressure?

Yes, there are several alternative methods for finding air leaks, such as using infrared cameras, smoke pencils, or blower doors. Each method has its own advantages and limitations, so it is important to choose the most suitable method for the specific building and situation.

Similar threads

  • Mechanics
Replies
9
Views
2K
Replies
10
Views
1K
Replies
31
Views
3K
  • Mechanics
Replies
12
Views
2K
Replies
3
Views
4K
Replies
4
Views
1K
Replies
3
Views
1K
  • Mechanics
Replies
4
Views
2K
Replies
9
Views
1K
Back
Top