In summary: Are you looking for a particular dryness value or the method to calculate it?In summary, the conversation revolves around determining the relative humidity, dew point, and moisture content/accumulation at the exit of a three-stage air compressor with a compression ratio of 205. The partial pressure of water vapour increases during compression and decreases during expansion, but no condensation occurs at the compressor outlet due to the high air temperature. The methodology for calculating the condensate value is provided, using the specific humidity of air at input and output conditions. The dew point temperature is derived from the saturation property table using the saturation pressure. The IAPWS Formulation 1995 is used for accurate calculations of ambient conditions.
  • #1
hail_thy_gt
18
0
Hello all,

Would appreciate some guidance here.

I have an air compressor compressing ambient air to 3000 psi into a 425cu-in tank. I have the volumetric flow rate at the exit. If I was looking for relative humidity, dew point, and moisture content/accumulation at the exit, how would I go about doing so.

The air would then be expanded from 3000 psi to 600 psi, how would I get the same information again?

I'm trying to evaluate the size of the moisture separator and heat exchanger needed to keep the system out of moisture by getting those values.

Thank you in advance.
 
Engineering news on Phys.org
  • #2
Hi,
First arrive at the air temperature and Relative humidity at the compressor inlet. Also arrive at the pressure dew point required for your application.
From the saturated water vapour property table, note down the partial pressure of water vapour at the air temperature and Rh
As the air is compressed, the partial pressure of water vapour increases by compression ratio and temperature of air increases. Because of increase in partial pressure of water vapour, the vapour condenses.
Cool the air to the temperature, at the line pressure which is the pressure dew point. Air will be saturated athis temperature.
As the air expands to the application pressure, partial pressure of water vapour decreases and thus relative humidity decreases.

I have enclosed a file for reference
 

Attachments

  • Copy of compressor.xlsx
    19.8 KB · Views: 890
  • #3
Sakthi1267,

Thank you for the response. I've pulling hair for something simple(I think). But, I wanted to add that the compressor is a three stage compressor, which spits out the air at 225 deg C. Is it safe assume then that at exit the humidity is 100%?
 
  • #4
Hail,

The compression ration for the compressor is 3014.7/14.7 Psi( 1 atm = 14.7 psi) = 205. Let us assume air at the inlet is 37 degree c And 95% Rh.

Partial pressure of water vapour at 37 C , 95 % Rh = 5.8 Kpa,
The partial pressure of water vapour increase by compression ratio times = 205 * 5.8 = 1189 Kpa.

The saturation temperature of water vapour for 1189 kpa = 187 C

In your case the air temperature at outlet is 225 C. As air temperature is higher than saturation temperature, there will not be any condensation happening at compressor outlet.

As the air expands from 3014 psi to 600 Psi(application pressure), the partial pressure of water vapour decreases. by expansion ratio which is = 3014/600 = 5.02

Partial pressure of water vapour at 600 Psi air pressure = 1189/5 = 237. Kpa
saturation temperature corresponding to 237 kpa= 125 C

If your application temperature is less than 125 C, condensation will happen.
 
  • #5
Sakthi,

That was very well put. I understand the system a little better. To add though, I had mistyped the temp, it's in fact 225F and not 225C. So, condensate will occur after the compression. I'm trying to determine the actual condensate quantity of accumulation or at least the rate.

Can I just obtain the absolute humidity in g/m^3 at the exit temperature(225F) and multiply by flow rate, Since RH is 100% at exit.

And, if correct, would similar path be warranted for expansion?
 
  • #6
Hail,

The product of absolute humidity and flow rate will provide you water vapor content of air at 225 F. It will not provide you the actual condensate value.
Here is a methodology which can be followed to calculate the condensate value.
Specific humidity of air at input condition (37 C, Rh 95%)= 0.66 Pw/(P-Pw) – Kg of water vapour / Kg of dry air.
Pw - Partial pressure of water vapor
P – Air pressure.
= 0.66 * (5861.5)/(100000-5861.5)
=41 g/kg of air – Note 1

At the compressor outlet, (107 C,Rh 100%) presssur 3000 Psi= 0.66 Pw/(P-Pw) – Kg of water vapour / Kg of dry air
Pw = 143.3 Kpa
P = 3000 Psi = 20684 Kpa
= 0.66 (143.3/(20684-143.3)
= 4.6 g/kg of air. – Note 2

Total condensate = Note 1- Note 2
= 41 - 4.6
= 36.4 g/Kg of dry air

Multiply this value with mass flow rate of dry air.
 
  • #7
dew pt temperature

hail,

How did you calculate the dew point temperature, you have used the formula, i am not able to understand.

But the calculation on condensate mass is correct.

Generally dew point temperature will be derived from saturation property table if we know the saturation pressure.
 
  • #8
Sakthi,

Thanks for getting back. The formula used is conducted by W. Wagner and A. Prub called "The IAPWS Formulation 1995 for the Thermodynamic Properties of Ordinary Water Substance for General and Scientific Use" in the Journal of Physical and Chemical Reference Data. I ran a few data points, and they were sufficiently accurate. This allows me to input certain ambient conditions, and now have to worry about running through the tables repeatedly.
 
  • #9
Hail,

What is your requirement for dryness value at the application.
 

Related to Relative Humidity and Dew Point after compression

What is relative humidity?

Relative humidity is a measure of the amount of water vapor present in the air compared to the maximum amount of water vapor the air can hold at a given temperature. It is expressed as a percentage and is affected by changes in temperature and the amount of water vapor in the air.

How is relative humidity affected by compression?

When air is compressed, its temperature increases and its capacity to hold water vapor also increases. This results in a decrease in relative humidity, as the ratio of water vapor to maximum capacity changes. The higher the compression, the greater the decrease in relative humidity.

What is the dew point?

The dew point is the temperature at which the air becomes saturated with water vapor, meaning that it can no longer hold any more water vapor. It is a measure of the amount of moisture in the air and is an important factor in determining the likelihood of precipitation.

How is the dew point affected by compression?

Similar to relative humidity, the dew point is also affected by compression. As air is compressed, its temperature increases, which can cause the dew point to increase as well. This means that the air can hold more water vapor before reaching saturation, resulting in a higher dew point.

What is the relationship between relative humidity and the dew point?

The relative humidity and the dew point are both measures of the amount of water vapor in the air. However, while relative humidity compares the actual amount of water vapor to the maximum capacity, the dew point is the temperature at which the air becomes saturated. As the relative humidity increases, the dew point also increases, indicating a higher likelihood of precipitation.

Similar threads

  • Mechanical Engineering
Replies
18
Views
3K
  • Classical Physics
Replies
3
Views
818
  • Mechanical Engineering
Replies
5
Views
2K
Replies
1
Views
1K
  • Mechanical Engineering
Replies
3
Views
1K
  • Mechanical Engineering
Replies
20
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Mechanical Engineering
Replies
5
Views
2K
Replies
6
Views
2K
Replies
5
Views
1K
Back
Top