Hi, I have a power systems protection assignment and I wanted to get some simple calcs verified.
XFMR - 30MVA, 132kV:22kV; Star/Delta respectively. star neutral is floating, not that it matters for this part.
reactance is 8% and resistance is 0.5% on the 30MVA base.
Basically I am trying to choose CT's and I don't want them saturated so I need the max line current (obviously the XFMR will trip on OC so I need max current up to 140%30MVA = 42MVA)
I have: [tex] I= \frac{42MVA}{\sqrt{3}*22kv} = 1.102kA [/tex] on the LV delta side. I'm not sure if this is correct though? why have the specified the transformer impedance?
I also need the max line current on the star side for diff protection but I think that that should just be reduced by the turns ration,,,, may have to account for the star delta configuration?
Thanks for any help.
XFMR - 30MVA, 132kV:22kV; Star/Delta respectively. star neutral is floating, not that it matters for this part.
reactance is 8% and resistance is 0.5% on the 30MVA base.
Basically I am trying to choose CT's and I don't want them saturated so I need the max line current (obviously the XFMR will trip on OC so I need max current up to 140%30MVA = 42MVA)
I have: [tex] I= \frac{42MVA}{\sqrt{3}*22kv} = 1.102kA [/tex] on the LV delta side. I'm not sure if this is correct though? why have the specified the transformer impedance?
I also need the max line current on the star side for diff protection but I think that that should just be reduced by the turns ration,,,, may have to account for the star delta configuration?