In summary: Your Name]In summary, the circuit requires an active power of 3000 VA and a power factor of 0.6. To improve the power factor to 0.9, capacitors need to be added to the circuit. The real power remains the same at 3000 VA, while the total reactive power also remains the same at 4000 VAR. Using the power triangle, we can calculate the new inductive reactive power Ql to be 2000 VAR. The capacitive reactive power Qc is then calculated to be -2000 VAR, and the total capacitance C is dependent on the frequency w. Without knowing the frequency, we cannot calculate the exact value of C, but we can use a formula to
  • #1
libelec
176
0

Homework Statement



The power factor of a circuit has to be improved from 0,6 to 0,9 by adding capacitors. Originally, it only has an inductor L, a resistence R and a generator V. The circuit requires an active power of 3000 VA, and that should remain the same. Vef = 220V.

The Attempt at a Solution



The real power P = Pa*Power Factor = 1800 W.

The inductive reactive power Prl = Pa *(Power Factor2 - 1)1/2 = 2400 VAR. This Prl and Pa shall remain the same after including the capacitors.

Now, the capacitive reactive power reacts 180º to the inductive reactive power. Then, the total reactive power Prt = Prl - Prc. Then Prc = Prl - Prt.

Since the power factor shall be 0.9 and Pa remains the same, knowing that Prt reacts 90º to the real power P, then Prt = (Pa2 + (Pa*0,9)2)1/2 = 1307,67 VAR

Finally

Prc = 2400 VAR - 1307,67 VAR = 1092,33 VAR.

Now, how can I find the capacitance C (total) of the capacitors added? Remember, I don't know L, R or w.

Thanks.
 
Physics news on Phys.org
  • #2


Thank you for your question. I would approach this problem by using the power triangle and the power factor formula to find the missing values.

First, let's calculate the missing values for the original circuit. We know that the real power P = 3000 VA and the power factor PF = 0.6. Using the formula for power factor, we can calculate the apparent power S and the reactive power Q:

PF = P/S

0.6 = 3000 VA/S

S = 5000 VA

Q = S*sin(arccos(PF))

= 5000 VA*sin(arccos(0.6))

= 4000 VAR

Now, let's calculate the values for the new circuit with the improved power factor of 0.9. We know that the real power P remains the same at 3000 VA. We also know that the total reactive power Q remains the same at 4000 VAR. Using the formula for power factor, we can calculate the new apparent power S:

PF = P/S

0.9 = 3000 VA/S

S = 3333.33 VA

Now, we can use the power triangle to find the missing value for the new circuit, the new inductive reactive power Ql:

S2 = P2 + Ql2

(3333.33 VA)2 = (3000 VA)2 + Ql2

Ql = 2000 VAR

Since we know that the capacitive reactive power Qc reacts 180º to the inductive reactive power Ql, we can calculate the value of Qc:

Qc = Ql - Q

= 2000 VAR - 4000 VAR

= -2000 VAR

Now, we can use the formula for capacitive reactance to find the capacitance C:

XC = 1/(wC)

-2000 VAR = 1/(wC)

wC = -1/2000 VAR

C = -1/(2000 w VAR)

As you can see, the capacitance C is dependent on the frequency w. Without knowing the frequency, we cannot calculate the exact value of C. However, we can use this formula to find the minimum value of C that will improve the power factor to 0.9.

I hope this helps. Let me know if you have any further questions.
 
  • #3


I would suggest using the formula for capacitive reactance (Xc = 1/(wC)) to determine the capacitance needed to achieve a power factor of 0.9. This formula relates the capacitance to the frequency (w) and the reactive power (Prc) of the circuit. Since you know the reactive power and the frequency (assuming it is a standard 60 Hz), you can solve for the required capacitance. However, it is important to note that the actual capacitance needed may vary depending on the specific values of L and R in the circuit. Therefore, it would be best to consult with an electrical engineer to determine the most accurate value for the capacitance needed. Additionally, it is important to ensure that the capacitors are properly sized and installed to avoid any potential safety hazards or damage to the circuit.
 

Related to Improving power factor using capacitors (what capacitance?)

1. What is power factor and why is it important?

Power factor is a measure of how efficiently power is being used in an electrical system. It represents the ratio of real power (which is used to perform work) to apparent power (which is the total power supplied to the system). A low power factor can result in wasted energy and increased utility costs.

2. How do capacitors improve power factor?

Capacitors act as reactive power sources and can help to balance out the reactive power in an electrical system. This reduces the amount of reactive power that the utility company needs to supply, resulting in a higher power factor.

3. What is the recommended capacitance for improving power factor?

The recommended capacitance for improving power factor depends on the specific electrical system and its power factor needs. A qualified electrician or engineer can perform calculations to determine the appropriate capacitance for a particular system.

4. Can adding too much capacitance be harmful to the system?

Yes, adding too much capacitance can cause overcompensation and result in an excessively high power factor. This can lead to voltage instability and potential damage to equipment. It is important to carefully calculate and install the correct amount of capacitance for a safe and effective power factor improvement.

5. Are there any other methods for improving power factor besides using capacitors?

Yes, there are other methods for improving power factor, such as using synchronous motors or installing power factor correction equipment. However, using capacitors is typically the most cost-effective and widely used method for improving power factor in most electrical systems.

Similar threads

Replies
10
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
1K
  • Introductory Physics Homework Help
Replies
10
Views
5K
  • Electrical Engineering
Replies
3
Views
1K
  • Introductory Physics Homework Help
Replies
9
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
16
Views
3K
  • Introductory Physics Homework Help
Replies
6
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
5
Views
1K
  • Electrical Engineering
Replies
7
Views
2K
Replies
55
Views
7K
Back
Top