How to find a suitable value for a neutral resistance?

In summary: R x I = 430 volts ).In summary, under normal operating conditions the fault current at the motor will be reduced to below 1014.15 amps, and the voltage rise at the motor will be limited to 430 volts.
  • #1
Neil Hayes
15
2

Homework Statement

.
[/B]
An 11kv motor is fed by cables from a transformer via switchgrear, having a phase impedence of 0.3 + j0.3 ohm. The Earth return path to the transformer neutral has a resistance of 0.42 ohm. Determine a suitable value of neutral resistance if the voltage rise at the motor in the event of an Earth fault at the motor is not to exceed 430 v

Hi there folks!

I would be very grateful for some suggestions in relation to the question above. I have asked my tutor for information on what exactly is being asked. The course material is vague and this was my best attempt at solving the problem. When I sent the attached pdf to my tutor they just replied :

Neutral resistor = Resistance path - 0.72

To me this seems too easy and also doesn't tie in with the information given in the associated lessons etc.

Maybe I'm on the right path but I'm just a bit unsure.

I would really appreciate any ideas :)

Neil
 

Attachments

  • Course work.pdf
    243.2 KB · Views: 245
Last edited by a moderator:
Physics news on Phys.org
  • #2
I think you need to start with a diagram showing the impedances.

A transformer on the 11 kV side is normally a wye (or star) connection.

The neutral resistor is connected from the neutral of the transformer to ground (earth).

Write the equations for the fault current with the neutral resistor and then for the voltage rise at the motor.

I'm not sure what you 430/0.72 represents. Did you mean 0.78 instead?
 
  • Like
Likes Neil Hayes
  • #3
magoo said:
I think you need to start with a diagram showing the impedances.

A transformer on the 11 kV side is normally a wye (or star) connection.

The neutral resistor is connected from the neutral of the transformer to ground (earth).

Write the equations for the fault current with the neutral resistor and then for the voltage rise at the motor.

I'm not sure what you 430/0.72 represents. Did you mean 0.78 instead?

Hi there Magoo,

Thanks a million for the reply to my post :)

There is an example in my lesson notes and if I was to follow the process it would go as follows ( using the values given in the question ).

Impedance of cables feeding the motor and the Earth return path to the transformer is :

Z = 0.72 + j0.3 which gives us 0.78 ohms

In the event of an Earth fault at the motor given this Impedance value we will have a Fault Current of 6350/.78 = 8141 amps

The cables that feed the motor from the transformer have an Impedance of .424 ohms

We need our fault current to be reduced to 430/.424 = 1014.15 amps

So ...

6350/1014.15 gives us a resistance or 6.26 ohms

What I'm thinking I need to do now is take our original 0.78 ohms which is the Impedance of the original system and take that from our newly found figure of 6.26 ohms to give us a value of 5.48 ohms.

A neutral earthing resistor with a value of 5.48 ohms needs to be added to the system.

This is what the information in the lesson would lead me to think anyway.

Does this make sense?

Neil
 
  • #4
Where did you get the value of 0.424? You need to show your work.

Since you didn't sketch a one-line diagram, see if this agrees with what you had in mind:

upload_2017-4-8_15-48-51.png
 
  • #5
magoo said:
Where did you get the value of 0.424? You need to show your work.

Since you didn't sketch a one-line diagram, see if this agrees with what you had in mind:

View attachment 134356

Hi again Magoo,

Apologies for not including a drawing. I will hand draw out one tomorrow and post it on the thread here. I need to look at my notes to see if your drawing is similar to what I have.

The 0.424 ohms from above was the impedance of the cables from the transformer to the motor. The question tells me that this section has an Impedance of :

Z = 0.3 + j0.3. The square root of 0.3^2 + 0.3^2 is equal to 0.424. If we have a current of 1014.15 then the voltage rise at the motor will be R x I ( 0.424 x 1014.15 = 430 volts )
 
  • #6
Your 0.424 ohms represents the cable impedance only. Under a ground fault, the fault path includes the cable impedance plus the Earth return. It looks like you neglected that.

It also looks like you neglected the reactance when you came up with 6.26 ohms.
 
  • #7
magoo said:
Your 0.424 ohms represents the cable impedance only. Under a ground fault, the fault path includes the cable impedance plus the Earth return. It looks like you neglected that.

It also looks like you neglected the reactance when you came up with 6.26 ohms.

Please see attached photo for the impedance diagram which shows the system prior to the addition of the neutral earthing resistor.

2017-04-13 09.48.21.jpg


The figures that I've written out are relate to fault conditions that are set out in the question.

On the right hand side I have 3419 V which is the potential difference from the motor area and the transformer. In order to reduce this potential difference to the 430 V asked for in the question I calculated that we need to reduce the current to 1024 amps (6350/.42).

We have a phase voltage of 6350 which I'm dividing by the 1024 and this gives me 6.2 ohms.

This 6.2 ohms will be the Impedance of the system with the neutral earthing resistor included so then to find the resistance value I then go down this route.

Z^2 = R^2 + X^2

6.2^2 = R^2 + 0.3^2

R^2 = 38.35

R = 6.19 ohms

From our original system we had a resistance of 0.72 ohms so I believe the value for the neutral earthing resistor is the 6.19 - 0.72 = 5.47 ohms

The information in is both vague and limited at times in the notes I have for the distance learning course which I'm doing.

The process I've used above is the same as that which I have been shown in my notes. The problem with the course notes is that it does the problem and gives the the final answer as an earth path impedance. I have found that to be 6.2 ohms ( using the method in my notes ) but as the questions specifically asks for a '' suitable value of neutral resistance ''

My apologies for the delay in replying to your last reply. I'm having trouble with my Laptop :( The appreciate you taking the time to try and point me in the right direction.

Neil
 
  • #8
Hi there Magoo,

It seems that my last post seems to be the correct way of going about the problem. I won't know for sure as I've to submit my work tomorrow but I'll let you know. Thanks again for your help to date!

Neil
 
  • #9
w/o the neutral resistor

Zphase = 0.3 + j 0.3

Zearth return = 0.42

For a phase to Earth fault, Z = 0.72 + j 0.3 |Z| = 0.78 ohms
Isc = V / Z = 6350 / 0.78 = 8141 A
Vacross motor = 6350 V
With neutral resistor

Want Vacross motor = 430

Need to reduce the sc current to

430/6350 * 6350/0.78 = 551.3 A
To do so requires an impedance of 11.52 ohms
You already have 0.72 + j 0.3 or 0.78 ohms
Need to solve for R that results in an impedance of 11.52 ohms

I just took 0.72 + R + j 0.3 and tried a few values for R that results in a Z of 11.52
I get an R of around 11 ohmsYou could also just neglect the X term and it will be a bit easier.
 
  • #10
Neil,

Good luck tomorrow and please post what you find out.
 
  • Like
Likes Neil Hayes
  • #11
magoo said:
Neil,

Good luck tomorrow and please post what you find out.

Will do and thanks again for your time to date :)
 
  • #12
Neil Hayes said:
Will do and thanks again for your time to date :)

Hi there Magoo,

I just got my results back from the assignment. I submitted my effort on post no 8 and got it correct. I got a distinction on the assignment so I'm well chuffed. Only another 100 to go lol ( well it fell like 100 anyway! )

Thanks for taking the time to work with me on the site here!

Neil
 
  • #13
That is terrific! Your perseverance paid off.
 
  • Like
Likes Neil Hayes
  • #14
magoo said:
That is terrific! Your perseverance paid off.

It sure did. Thanks again :smile:
 

Related to How to find a suitable value for a neutral resistance?

1. How is the neutral resistance value determined?

The neutral resistance value is typically determined by conducting a series of tests and calculations based on the specific circuit and its components. It also depends on the desired level of neutrality and the intended use of the circuit.

2. What factors should be considered when selecting a neutral resistance value?

The factors that should be considered when selecting a neutral resistance value include the type of circuit, the voltage and current levels, the impedance of the other components, and the desired level of neutrality. It is also important to consider safety and efficiency of the circuit.

3. How does the neutral resistance value affect the performance of a circuit?

The neutral resistance value can affect the performance of a circuit by influencing the flow of current, the voltage levels, and the overall stability of the circuit. A suitable neutral resistance value is necessary for a circuit to function properly and efficiently.

4. Can the neutral resistance value be adjusted?

Yes, the neutral resistance value can be adjusted by using different resistors or by changing the configuration of the circuit. However, it is important to carefully calculate and test the new value to ensure it is suitable for the circuit.

5. How can I determine if the chosen neutral resistance value is suitable?

You can determine if the chosen neutral resistance value is suitable by conducting tests and measurements on the circuit. This will help to ensure that the circuit is functioning properly and safely, and that the desired level of neutrality is achieved.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
5K
  • Electrical Engineering
Replies
1
Views
959
  • Electrical Engineering
Replies
15
Views
11K
  • Advanced Physics Homework Help
Replies
1
Views
22K
  • Calculus and Beyond Homework Help
Replies
2
Views
7K
  • Introductory Physics Homework Help
Replies
4
Views
38K
  • MATLAB, Maple, Mathematica, LaTeX
Replies
1
Views
3K
Back
Top