H Is a low, leading power factor causing our subsea power distribution issues?

In summary, the conversation is about a subsea power coupling module that provides isolated 550 VAC to a subsea control pod on a well in the Gulf of Mexico. The power line, called an umbilical, runs for approximately 50 miles from the power unit on the platform to the subsea field. The coupling unit contains an Integra power meter and a Bender A-ISOmeter IRDH375 which monitors insulation resistance. The power meter documentation states that the power factor should be between 1 and -1, but in this case it is showing a low and leading power factor of .46. This has caused a low insulation alarm and resulting trip in the supply. The cause of this issue is unknown and may be related to
  • #1
Screamtruth
5
0
Gents, this will be a long winded.

We have a subsea power coupling module that provides isolated 550 VAC to our subsea control pod on a well in the Gulf of Mexico. The power line is actually termed as an umbilical, with the two cores or wires running from our power unit on the platform to the subsea field. The length is in the order of 50 miles or so.

In our coupling unit we have an Integra power meter which supplies our voltage, current, THD, power factor, apparent power, reactive power, etc, data. We also have a Bender A-ISOmeter IRDH375 that monitors our insulation resistance using Adaptive Pulse Measurement AMP. The ISOmeter has an alarm output contact that opens our contactor in the event of an low (600kOhm) insulation reading. These faults are common in older fields such as this, but this seems to be an exception.

The power meter documentation for the Integra 1350 says the power factor screen will display any number between 1 and -1, i.e. -.76 which would indicate a power factor of 76 that is lagging (inductive reactance I assume). Our situation is that the power factor is shown to be a .46, which is indicative of a LEADING power factor, and very low at that. The norm for our systems is around -.67 to -.78. I was assuming at first that the power factor was leading due to the large amount of capacitance due to the length of the umbilical. I know that our lines are usually in the negative range in respect to power factor due to the step up transformer in the coupling unit and the step down transformer in the subsea control unit. There are no other components in the line other than the two transformers and 1 large varistor in the coupling unit to suppress transients.

The problem is a low insulation alarm, and resulting trip in our supply. We cannot seem to correlate this event with any other. The power coupling unit itself is run off a UPS with a stable and conditioned supply. We do see a 20 volt increase in the subsea control unit, followed by a drop of the power factor from .46 to .35, then we will see the ISOmeter go into alarm and trip the circuit.

Any ideas what could cause such a low, leading power factor? What would be the effects of a low, leading power factor? Would there be any connection between the low power factor and a low insulation resistance, or could the varistor be failing and cause such a low insulation resistance?
 
Engineering news on Phys.org
  • #2
We have a engineer member here, stewartcs, that is involved with subsea systems. You might want to PM him to see if he might have experienced this situation.
Would there be any connection between the low power factor and a low insulation resistance...
Yes. I would think so, but I'm no expert here.
 
  • #3
Thank you sir.



I will PM.
 
  • #4
Screamtruth said:
Gents, this will be a long winded.

We have a subsea power coupling module that provides isolated 550 VAC to our subsea control pod on a well in the Gulf of Mexico. The power line is actually termed as an umbilical, with the two cores or wires running from our power unit on the platform to the subsea field. The length is in the order of 50 miles or so.

In our coupling unit we have an Integra power meter which supplies our voltage, current, THD, power factor, apparent power, reactive power, etc, data. We also have a Bender A-ISOmeter IRDH375 that monitors our insulation resistance using Adaptive Pulse Measurement AMP. The ISOmeter has an alarm output contact that opens our contactor in the event of an low (600kOhm) insulation reading. These faults are common in older fields such as this, but this seems to be an exception.

The power meter documentation for the Integra 1350 says the power factor screen will display any number between 1 and -1, i.e. -.76 which would indicate a power factor of 76 that is lagging (inductive reactance I assume). Our situation is that the power factor is shown to be a .46, which is indicative of a LEADING power factor, and very low at that. The norm for our systems is around -.67 to -.78. I was assuming at first that the power factor was leading due to the large amount of capacitance due to the length of the umbilical. I know that our lines are usually in the negative range in respect to power factor due to the step up transformer in the coupling unit and the step down transformer in the subsea control unit. There are no other components in the line other than the two transformers and 1 large varistor in the coupling unit to suppress transients.

The problem is a low insulation alarm, and resulting trip in our supply. We cannot seem to correlate this event with any other. The power coupling unit itself is run off a UPS with a stable and conditioned supply. We do see a 20 volt increase in the subsea control unit, followed by a drop of the power factor from .46 to .35, then we will see the ISOmeter go into alarm and trip the circuit.

Any ideas what could cause such a low, leading power factor? What would be the effects of a low, leading power factor? Would there be any connection between the low power factor and a low insulation resistance, or could the varistor be failing and cause such a low insulation resistance?

Are you having an intermittent problem with your isometer tripping or is constantly tripped?

Have you ran a self-test on the isometer?

Have you changed the measuring principle from AMP to DC to see if it still trips?

Have you adjusted the set point for an insulation fault to see if it still trips? (There is usually some leeway with the set point.)

All the problems I've experienced with subsea cables have been for drilling control systems so they are significantly shorter in length (up to 13,500 feet). However, almost always the isometer faults were due to water ingress in the cable or connector. Unfortunately, it sounds like your cable is not retrievable (perhaps a production unit instead of drilling system) so it may be difficult to troubleshoot. Do you have some more details on the cable (manufacturer and spec) and the control system (e.g. type of load like, manufacturer)?

CS
 
  • #5
The fault is intermittent, which makes this all the more difficult to define.

I am not too sure on the operation of the Bender, but I had assumed, possibly incorrectly, that transposing a DC signal may have been a poor choice by introducing DC into the end load, which is an isolation/step down transformer. I am not too familiar with the Bender measurement circuit, but I assume that their unit loaded to prevent any issues with a DC measurement. Sounds like a good idea to try.

I guess my main question would be regarding the presence of a leading power factor. With the load being a transformer, I would assume that the power factor would resemble that of a normal power distribution circuit, thus being largely inductive in nature. Could the capacitance of a long power line overcome the inductive reactance of the load?
 
  • #6
Screamtruth said:
Could the capacitance of a long power line overcome the inductive reactance of the load?

I suppose it is possible. 50 miles is a long cable so the capacitance may very well be that high. But again, I've never dealt with cables that long. Check with the manufacturer for the cable specs. They should be able to tell you what to expect from it.

Good luck.

CS
 

Related to H Is a low, leading power factor causing our subsea power distribution issues?

1. What is subsea power distribution?

Subsea power distribution refers to the distribution of electrical power from a central source to various subsea equipment and devices, typically located on the ocean floor. This technology is used in various industries such as offshore oil and gas, marine renewable energy, and telecommunications.

2. How does subsea power distribution work?

Subsea power distribution systems typically consist of a power source, such as a subsea transformer or subsea power cable, and a network of subsea distribution hubs and cables that deliver power to different subsea equipment. The power is transmitted through either direct current (DC) or alternating current (AC) depending on the specific application.

3. What are the benefits of subsea power distribution?

Subsea power distribution offers numerous benefits, including increased efficiency, reduced cost and maintenance, and improved reliability. By distributing power closer to the subsea equipment, there is less energy loss and fewer power outages. Additionally, subsea power distribution eliminates the need for large and expensive surface infrastructure, making it a more cost-effective option.

4. What are some challenges of subsea power distribution?

One of the main challenges of subsea power distribution is the design and maintenance of the system in harsh and corrosive underwater environments. Additionally, subsea power cables are susceptible to damage from underwater hazards such as fishing activities and natural disasters. Ensuring the reliability and safety of the system is also a significant challenge.

5. What are some current developments in subsea power distribution?

There are ongoing developments in subsea power distribution, including the development of more efficient and reliable power cables, advancements in subsea transformers and distribution hubs, and the integration of renewable energy sources. There is also a growing focus on using digital technologies such as sensors and remote monitoring systems to improve the operation and maintenance of subsea power distribution systems.

Similar threads

Replies
9
Views
2K
Replies
4
Views
3K
  • Electrical Engineering
Replies
13
Views
6K
  • Electrical Engineering
Replies
1
Views
3K
Replies
5
Views
3K
  • Electrical Engineering
Replies
2
Views
4K
Replies
1
Views
641
  • Sci-Fi Writing and World Building
Replies
2
Views
2K
Replies
4
Views
3K
  • Aerospace Engineering
Replies
2
Views
7K
Back
Top