Frequency Vs Max Load current (Motor)

In summary: I have the correct VFD...change the frequency on the VFD without changing the voltage?Yes - you can change the frequency on the VFD without changing the voltage.
  • #1
abhipatel
30
0
Have a 15 HP motor whose full load current (@ 50 Hz - India norms) is calculated at around 21 Amps. Have added a VFD (Variable Frequency drive) and would like to always run the machine @ 90% of full load current for maximum efficiency.

Can anyone assist in helping me calculating full load current as frequency is changed? What would be the full load current @ 40 Hz, 35 Hz and 45 Hz?

Thanking everyone in advance. Appreciate the help, time and effort.
 
Engineering news on Phys.org
  • #2
This is a 3ɸ induction motor, is it? I looked over a few articles, and it seems it's not particularly straight-forward. For example, are you intending that the motor start on a reduced frequency under full load?

Generally, where variable frequency control is used to slow a motor, it is also necessary to reduce the voltage proportionately to avoid magnetic saturation, increased losses, and aggravating high pitched noise from the motor. See http://www.most.gov.mm/techuni/media/EP05028_6.pdf

My reading of this is that as you lower the frequency, you must simultaneously reduce the voltage so as to maintain the motor's current constant at its rated value (or, in your case, at 90% of that value).

(Should you intend increasing the frequency to speed the motor up, this is going to be a different kettle of fish.)

I'll monitor this thread to see whether someone with first-hand experience can help.
 
Last edited by a moderator:
  • #3
Full load current is full load current. It is a constant, based on the physical properties of the motor.
 
  • #4
all i want to ensure is i do not lose my blast wheel efficiency which is being run by the motor. All experts recommend running the wheel @90% to get max utilization.

Blasting is controlled by amperes - with 50 HZ i can get 19-20 Amps easy (90% of 21 A) but when i bring the freq. down using VFD to 35 Hz it is hard to get my amps back to 19-20 Amps...not much of a electrical guy but was thinking there should be some relation.

Am afraid to push the amps back to 19 Amps @ 35 Hz might overload the motor...

Just trying to explain my reasoning...then there are the experts who know much better...
 
  • #5
Is this a 3ɸ induction motor?
 
  • #6
Yes, reducing the frequency will reduce the amperage because you're reducing the mechanical power output.
 
  • #7
ty russ...i believe the same too...how would we calculate what reduction is achieved though?
 
  • #8
If your load torque is constant, then reduction in speed (w) results in reduction in output power (P = T*W), almost linearly with speed. So, If you did keep the Voltage constant, then current would reduce linearly as well. (Not quite linearly, but its cos(phi) component should reduce linearly with speed).
However, like in most VFD, if voltage is decreased with frequency (speed), then it appears that the current shouldn't decrease but remain constant.
abhipatel said:
Am afraid to push the amps back to 19 Amps @ 35 Hz might overload the motor...
Do you have a separate control of frequency and Voltage or Are they linked?
How exactly do you plan to 'push the amps back @ 35Hz' ?
 
  • #9
abhipatel said:
ty russ...i believe the same too...how would we calculate what reduction is achieved though?
It depends entirely on the nature of the load. What is the load?
 
  • #10
NascentOxygen said:
Generally, where variable frequency control is used to slow a motor, it is also necessary to reduce the voltage proportionately to avoid magnetic saturation, increased losses, and aggravating high pitched noise from the motor. See http://www.most.gov.mm/techuni/media/EP05028_6.pdf

My reading of this is that as you lower the frequency, you must simultaneously reduce the voltage so as to maintain the motor's current constant at its rated value (or, in your case, at 90% of that value).
Only just noticed the reference I included above is nothing like I intended, seems I must have clicked on the wrong link. Here is a better reference, the torque graphs showing voltage being reduced proportionately as frequency is reduced, in order to maintain flux at design value.

http://itee.uq.edu.au/~mmme2104/Lecture%206a%20-%20VVVF%20IM%20Speed%20Control.pdf
 
Last edited by a moderator:
  • #11
I think that Nascent and Russ have nailed it. That little tutorial on VFD was great, by the way...

If i understand what is a "blast wheel", it is akin to a centrifugal pump but it's slinging a granulated abrasive instead of a fluid like water or air.

Do a search on "Fan Laws" and you'll find that the power to drive any pump varies with the square or cube of the speed depending whether mass flow rate changes...

so - at reduced speed, your V/F control keeps the motor's magnetizing current nearly constant
but the load current due to motor's mechanical load depends on the mechanical work being drawn by the blast wheel.
You may not be able to force full load current into that motor if it is lightly loaded because of the reduced speed.
Can I assume the abrasive's mass flow rate drops off at lower speed? Certainly its exit velocity would, hence power drawn from motor is also less .

Try controlling current by adjusting the abrasive feed rate(which controls mechanical work being done) instead of adjusting voltage( which just controls flux inside the motor).

all - is my thinking straight here? did i address right question?

anyhow if you force extra current into a lightly loaded motor by raising voltage, you make extra magnetic flux which overheats the iron, and in large machines can melt the corners off your stator laminations. Try a search on "fringing flux".
Forcing current up to 21 amps (rms not average) shouldn't hurt the copper provided the cooling fan is sized for lower speed operation, but you may well hurt the iron.
So Recall Thoreau's "Different Drummer". Let the motor draw just whatever current it needs to provide the required mechanical work.
old jim
 
Last edited:
  • #12
hmmmm one more thought - further reducing voltage below V/F ratio will increase slip hence stator current,
but be aware that also increases rotor current and you have no indication of rotor current or rotor temperature.
Were i were doing that to a motor that i owned, i'd keep it within rated slip as % of operating RPM. The fellows who designed that motor shaped the rotor bars for the flux they expected, so be cautious when changing that.
 

Related to Frequency Vs Max Load current (Motor)

What is the relationship between frequency and maximum load current for a motor?

The frequency of an alternating current (AC) supply is directly proportional to the maximum load current that a motor can handle. As the frequency increases, the maximum load current also increases. This relationship is known as the motor's frequency-current characteristic and is typically represented by a graph or table.

Why does the maximum load current increase with frequency?

The maximum load current increases with frequency because, as the frequency increases, the motor's speed also increases. This means that the motor has to work harder to maintain the same level of torque, resulting in a higher load current. Additionally, higher frequencies can cause more heat to be generated in the motor, which can also contribute to an increase in maximum load current.

How does the frequency affect the efficiency of a motor?

The frequency can have a significant impact on the efficiency of a motor. In general, as the frequency increases, the efficiency of the motor decreases. This is because higher frequencies can cause more energy to be lost as heat, resulting in a decrease in overall efficiency. Additionally, at higher frequencies, the motor may need to operate at a higher load current, which can also decrease efficiency.

Is there a limit to the maximum load current a motor can handle at a given frequency?

Yes, there is a limit to the maximum load current a motor can handle at a given frequency. This is because every motor has a maximum current rating, which is the maximum amount of current that the motor can safely handle without overheating or sustaining damage. This rating depends on various factors, including the motor's design, materials, and cooling mechanisms.

How can I determine the appropriate frequency and maximum load current for a specific motor?

The appropriate frequency and maximum load current for a specific motor can be determined by consulting the motor's datasheet or by using the motor's frequency-current characteristic graph or table. These resources will provide information on the motor's maximum current rating and its performance at different frequencies, allowing you to choose the most suitable frequency and load current for your application.

Similar threads

Replies
2
Views
811
  • Electrical Engineering
Replies
15
Views
758
Replies
2
Views
488
Replies
4
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Electrical Engineering
Replies
15
Views
3K
  • Electrical Engineering
Replies
7
Views
2K
Replies
23
Views
3K
  • Electrical Engineering
Replies
16
Views
4K
  • Electrical Engineering
Replies
1
Views
1K
Back
Top