Homework Statement


Dense No 1 grade of Douglas Fir-Larch, 6x12 is to be used as a simple beam spanning 10 feet with a 2 feet overhang. The beam has the loading shown in the sketch I've attached. Determine the maximum value of the concentrated load "P" to maintain the structural integrity associated with bearing. The beam rest on 4x12 members at both supports.

Homework Equations


fv= VQ/Ib
fb= Mc/I

fc[itex]\bot[/itex] = bearing/common area

The Attempt at a Solution



I found these for the 4x12:
S=73.83
I= 415.3
A=39.38
Q=72
c=6
fc[itex]\bot[/itex] =625
common area = 3.5(5.5)?
bearing=12031.25?

I'm not sure if this is right? So the max "P" would be 12031.25#?

or Fc[itex]\bot[/itex] = 625 for 2-4in boards and Fc[itex]\bot[/itex] = 730 for 5" and bigger

730= V/3.5x3.5 - V=8942.5
625= V/3.5x3.5 - V=7656.25
 

Attachments

  • draw.pdf
    18.6 KB · Views: 190
Last edited:
Physics news on Phys.org
  • #2
Wood tends to be quite strong in compression - think railroad ties - so the part of the structure that limits the load is not the 4X12 supports. You must determine the reactions at the supports, then determine the maximum moment in the beam. To determine the reactions, you should include the weight of the beam itself. Then adjust P so that the maximum allowable stress is attained.
 
  • #3
LawrenceC said:
Wood tends to be quite strong in compression - think railroad ties - so the part of the structure that limits the load is not the 4X12 supports. You must determine the reactions at the supports, then determine the maximum moment in the beam. To determine the reactions, you should include the weight of the beam itself. Then adjust P so that the maximum allowable stress is attained.

This is what I've came up with:

By adding 16,075# 5.75ft from R2
R1(10)+2000(1)=16075(5.75)+10000(5)
R1=14043.125
R2=14031.875

Fc allowable is 730 for Dense No1

729.51=14043.125/(3.5)(5.5) for R1
728.93=14031.875/(3.5)(5.5) for R2

So am I getting the correct answer?? Max allowable Load for P would be 16,075#
 
  • #4
I don't know where your 5.75 comes from, or your 16 075. But essentially, your method
for determining P based on allowable bearing pressure at the supports is ok. However , as noted in post 2, bending stress in the beam may control the design.
 
  • #5
PhanthomJay said:
I don't know where your 5.75 comes from, or your 16 075. But essentially, your method
for determining P based on allowable bearing pressure at the supports is ok. However , as noted in post 2, bending stress in the beam may control the design.

The 5.75 is the distance "P" Is from the R2 reaction or 4.25 from R1. 16075 is the load "P" in lbs plus the 1000#/1 on the beam that gives me my reactions on R1and R2.

Bending stress is fb? Allowable is Fb? I think I maybe over thinking this problem
 
  • #6
Oh I didn't realize that the distance from P to the supports was given...your sketch didn't show that . So yes you could put that 16 k load there and your support bearing stress is ok. But although the problem didn't ask about bending stresses, they soould be checked by calculating the max moment in the beam and the max bending stress fb vs the allowable bending stress Fb (about 1500 psi ?) and that may end up controlling the value of P.
 
  • #7
PhanthomJay said:
Oh I didn't realize that the distance from P to the supports was given...your sketch didn't show that . So yes you could put that 16 k load there and your support bearing stress is ok. But although the problem didn't ask about bending stresses, they soould be checked by calculating the max moment in the beam and the max bending stress fb vs the allowable bending stress Fb (about 1500 psi ?) and that may end up controlling the value of P.

The distance from P was not given, its what I calculated and solved for when I did my reactions.

I did the bending stresses and calculations this is what I came up with:

Fb=1550
fb=M/S =417.92psi
M=50652
S=121.2

So by my calculations it would hold
 
  • #8
There are a couple of issues here. Your value for the max moment is in foot pounds. This must first be converted to inch pounds. Beyond that, you seem to have chosen a location for P that yields equal left and right support reaction forces. Is the problem worded that way?
 

Related to Max "P" = 12031.25# or 8942.5#Calculating Max "P" for Douglas Fir-Larch Beam

1. What does "Max P" mean?

"Max P" refers to the maximum safe load or weight that a Douglas Fir-Larch beam can support without breaking or buckling. It is an important factor to consider when designing a structure or choosing a beam for a specific application.

2. How is "Max P" calculated for a Douglas Fir-Larch beam?

The calculation for "Max P" is based on the strength and stiffness properties of the beam material, as well as its dimensions. For Douglas Fir-Larch beams, the calculation takes into account the species' specific gravity, modulus of elasticity, and bending strength.

3. Why is Douglas Fir-Larch commonly used for beams?

Douglas Fir-Larch is a popular choice for beams in construction due to its high strength-to-weight ratio and its resistance to decay and insect damage. It is also readily available and cost-effective.

4. What factors can affect the "Max P" for a Douglas Fir-Larch beam?

The "Max P" for a Douglas Fir-Larch beam can be affected by several factors, including the quality and grade of the wood, the condition and moisture content of the wood, and any defects or imperfections in the beam. The beam's span and the type of load it will be supporting also play a role in determining the "Max P."

5. How can "Max P" be increased for a Douglas Fir-Larch beam?

The "Max P" for a Douglas Fir-Larch beam can be increased by using a higher grade or quality of wood for the beam, ensuring proper installation and support, and reducing the span or load on the beam. Strengthening techniques such as laminating or reinforcing the beam can also increase its "Max P."

Similar threads

  • Introductory Physics Homework Help
Replies
5
Views
3K
Back
Top