In summary, the conversation discusses a problem involving a small industry operating at 220 volts with a power factor of 0.8. The goal is to find the value of a capacitor that can be placed at the main voltage panel to correct the circuit to a unity power factor at a frequency of 60 Hz. The equations used to solve the problem are cosø = 0.8, P=VIcosø, and Xc = V/Ic. The solution involves finding the phasor current of IL and using its opposite imaginary component as Ic, which can then be substituted into the equation for capacitance. The expert recommends using the source voltage and current phasor to determine impedance or admittance.
  • #1
kaalad
5
0

Homework Statement



A small industry operates from 220 volts supplied by a utility. The small
industry represents a load to the utility that represents 22,000 watts and a power factor of 0.8.Determine the value of a capacitor placed at main voltage panel to correct the circuit to unity power factor. The supply frequency is 60 Hz.

Homework Equations



cosø = 0.8
P=VIcosø
Xc = V/Ic

The Attempt at a Solution



I was able to get 80A as a value for I using P=VIcosø but it does not have an imaginary component which is what I need to solve the problem. Can someone please tell me how I am supposed to get the imaginary component?
 
Physics news on Phys.org
  • #2
kaalad said:

Homework Statement



A small industry operates from 220 volts supplied by a utility. The small
industry represents a load to the utility that represents 22,000 watts and a power factor of 0.8.Determine the value of a capacitor placed at main voltage panel to correct the circuit to unity power factor. The supply frequency is 60 Hz.

Homework Equations



cosø = 0.8
P=VIcosø
Xc = V/Ic

The Attempt at a Solution



I was able to get 80A as a value for I using P=VIcosø but it does not have an imaginary component which is what I need to solve the problem. Can someone please tell me how I am supposed to get the imaginary component?

Hi kaalad, Welcome to Physics Forums.

Check your current calculation --- I don't see 80 A as the magnitude of the current.

It's helpful to know about power triangles, current triangles, and impedance triangles for AC calculations. It's also worth knowing that the the phase angle associated with the power is the same as that for the impedance (i.e. the power and impedance triangles are similar triangles).

If you know the magnitude of the current and the power factor then you can fill in the adjacent and opposite sides of the current triangle and hence write the current as a complex number (phasor). From there to the impedance is straightforward given that you known the source voltage.
 
  • #3
Thanks for replying :)

I did over the calculations and got 100 A as the current.

I also drew a current triangle and managed to get IL as 80 A and Ic as 60 A.
This is where I realized that what I actually need (well what i think I need) is the phasor current of IL.

What I learned was that for the unity power factor, the imaginary component of the total current IT should be 0. And IT = IL + Ic

Therefore, it seems that I may need to find the phasor current of IL as well and use the opposite of its imaginary part as Ic. For instance, if IL = 3 + j5, Ic would be equal to -j5 for a unity power factor.

The value of Ic would then be substituted into the equation Xc = V/Ic.
Xc would then be put into C = 1/(2∏fXC) to get the value of the required capacitance.

Sorry I didn't put all this in the original question but I was a bit confused as to what was needed and I was a bit sleepy :redface:

But in summary what I would like help with now is how to find the phasor current of IL. Of course, if you are aware of another way on how to solve the question I am open to suggestions.
 
  • #4
kaalad said:
Thanks for replying :)

I did over the calculations and got 100 A as the current.
Can you show your calculation? Which current value is that? The magnitude of the total current phasor or that of the real component only?

I also drew a current triangle and managed to get IL as 80 A and Ic as 60 A.
This is where I realized that what I actually need (well what i think I need) is the phasor current of IL.
Again, you should show your calculations so we can tell what it is you're calculating. Is IL the total load current? How do you arrive at Ic with the power triangle? (Assuming Ic is supposed to be the capacitor current?)

What I learned was that for the unity power factor, the imaginary component of the total current IT should be 0. And IT = IL + Ic

Therefore, it seems that I may need to find the phasor current of IL as well and use the opposite of its imaginary part as Ic. For instance, if IL = 3 + j5, Ic would be equal to -j5 for a unity power factor.

The value of Ic would then be substituted into the equation Xc = V/Ic.
Xc would then be put into C = 1/(2∏fXC) to get the value of the required capacitance.

Sorry I didn't put all this in the original question but I was a bit confused as to what was needed and I was a bit sleepy :redface:

But in summary what I would like help with now is how to find the phasor current of IL. Of course, if you are aware of another way on how to solve the question I am open to suggestions.
You can find the magnitude of the total current from the real power, the source voltage, and power factor as you stated in the first post. What value do you get for the magnitude of the current? Show your calculation.

A current triangle can then be created with this current value on the hypotenuse and using the power factor value to find the other side lengths: real current, imaginary current). That gives you the current phasor in rectangular form.

With the source voltage and current phasor you can determine the impedance, or more handy, the admittance...
 
  • #5
gneill said:
Can you show your calculation? Which current value is that? The magnitude of the total current phasor or that of the real component only?

Sorry! That's the total current value. BUT while I was typing it here i realized I did something wrong...again :frown: so what I put here is my new value.
I used I = P/Vcosø
= 22000/(22 x 0.8)
= 1250 A

So here are all the calculations based on this value (1250 A). Sorry again x.x

(I'm not sure how to draw a triangle here so I'll put it in words)
The Current triangle:
The hypotenuse is the total current, I = 1250 A
The angle was cos-1(0.8) = 36.9
The opposite side is the capacitive current, Ic
The adjacent side is the inductive current, IL

IL = cos(36.9) x 1250 = 0.8 x 1250 = 1000
Ic = sin(36.9) x 1250 = 0.6 x 1250 = 750

∴I = 1000 + j750 A

For unity power factor, we would want I = 1000
∴ Ic of the required capacitor would have to be -j750

So substituting |Ic| = 750 into |Xc| = |V|/|Ic|gives:
|Xc| = 220/750 = 0.2933

Then substituting |Xc| into C = 1/(2∏fXc) gives:
C = 1/(2∏ x 60 x 0.2933)
= 0.00904 F
= 904 μF

So the required capacitance is 904 μF.

Hopefully I made everything clear this time :/
Is this correct?
 
  • #6
kaalad said:
Sorry! That's the total current value. BUT while I was typing it here i realized I did something wrong...again :frown: so what I put here is my new value.
I used I = P/Vcosø
= 22000/(22 x 0.8)
= 1250 A
Right, except that the source voltage is 220 V, not 22 V. That means that rest of your current values (below) will be 10x too high. No worries, it's just a scaling issue that doesn't affect the basic procedure.

So here are all the calculations based on this value (1250 A). Sorry again x.x

(I'm not sure how to draw a triangle here so I'll put it in words)
The Current triangle:
The hypotenuse is the total current, I = 1250 A
The angle was cos-1(0.8) = 36.9
The opposite side is the capacitive current, Ic
The adjacent side is the inductive current, IL
Okay, bit of a problem there. The opposite side represents the REACTIVE current, that is, the imaginary portion of the current phasor, while the adjacent side represents the REAL current. There's no capacitor involved in the circuit yet.

IL = cos(36.9) x 1250 = 0.8 x 1250 = 1000
Ic = sin(36.9) x 1250 = 0.6 x 1250 = 750

∴I = 1000 + j750 A
Yup, just divide that current by 10.

For unity power factor, we would want I = 1000
∴ Ic of the required capacitor would have to be -j750

So substituting |Ic| = 750 into |Xc| = |V|/|Ic|gives:
|Xc| = 220/750 = 0.2933

Then substituting |Xc| into C = 1/(2∏fXc) gives:
C = 1/(2∏ x 60 x 0.2933)
= 0.00904 F
= 904 μF

So the required capacitance is 904 μF.
And, thanks to the one slip above being just a scaling issue which cancels out in the calculation, you've arrived at a correct value for the capacitance :smile:

Hopefully I made everything clear this time :/
Is this correct?

Just fix your voltage value as mentioned above and scale the currents accordingly and you'll be okay.
 
  • Like
Likes 1 person
  • #7
Whew! Thank you soooo much for your help and your patience! :smile:
 
  • #8
Just chiming in with another question...
Looking at the power triangle, if you adjust the power factor on a main unit generator, does it cause the reactive power and apparent power to change, while maintaining the real power?
 
  • #9
mudweez0009 said:
Just chiming in with another question...
Looking at the power triangle, if you adjust the power factor on a main unit generator, does it cause the reactive power and apparent power to change, while maintaining the real power?

All of the quantities are interrelated. Changing the phase angle of the source will change the "allocation" of the power available to real or imaginary components of the power in the load. Usually the method of changing the power factor of the source involves altering the load in some way (even if it's adding a "load" at the source side of a distribution network).
 
  • #10
gneill said:
All of the quantities are interrelated. Changing the phase angle of the source will change the "allocation" of the power available to real or imaginary components of the power in the load. Usually the method of changing the power factor of the source involves altering the load in some way (even if it's adding a "load" at the source side of a distribution network).

Well for the problem I am looking at, I must choose one that is maintained the same when changing the PF. So I imagined it was the real power that stayed the same. Because changing the angle, it has nothing to do with the adjacent leg of the angle.
 
  • #11
mudweez0009 said:
Well for the problem I am looking at, I must choose one that is maintained the same when changing the PF. So I imagined it was the real power that stayed the same.

Sure. But you would then choose the changes made accordingly. For example, you might have to change the source voltage along with the power factor.
 
  • #12
Here is what I used for the power triangle. I am not familiar at all with electric systems.

The main page showing power triangle, apparent/real/reactive power:
http://www.allaboutcircuits.com/vol_2/chpt_11/2.html

Using the side bar on the left to get to the "calculating power factor" page, I feel like my original answer is wrong. On this page it says:
For the purely resistive circuit, the power factor is 1 (perfect), because the reactive power equals zero. Here, the power triangle would look like a horizontal line, because the opposite (reactive power) side would have zero length.

For the purely inductive circuit, the power factor is zero, because true power equals zero. Here, the power triangle would look like a vertical line, because the adjacent (true power) side would have zero length.

So if at PF=1, its a horizontal line, and if at PF=0 its a vertical line, that means it is changing the true (horizontal) and reactive (vertical) lines. However, the apparent power (hypotenuse) changes with both of these changes. So I don't know how I'm supposed to pick a side that will remain the same when changing the PF..:confused:
 
  • #13
mudweez0009 said:
So if at PF=1, its a horizontal line, and if at PF=0 its a vertical line, that means it is changing the true (horizontal) and reactive (vertical) lines. However, the apparent power (hypotenuse) changes with both of these changes. So I don't know how I'm supposed to pick a side that will remain the same when changing the PF..:confused:

Why do you need to pick a side?

But supposing that you want to keep the real power the same despite changing the power factor, you may find that you have to adjust something else, such as the source voltage to make it so.
 
  • #14
Because that's what the problem asks for. Out of the 3 "sides" (or powers), they ask by changing PF, which two sides change, which one remains the same.
 
  • #15
mudweez0009 said:
Because that's what the problem asks for. Out of the 3 "sides" (or powers), they ask by changing PF, which two sides change, which one remains the same.

The power factor can be changed by adjusting the resistive or reactive parts of the load, or both. In "real world" practice the adjustment of power factor is usually done so as to maintain the real power to the load as a constant and reduce the reactive power (which produces no work and is thus wasteful for the generator to have to produce). The practical way to accomplish this is to place an additional purely reactive load in parallel with the original load in order to at least partially cancel out the reactance of the load. This brings the power factor closer to 1. So I suppose in this sense the "side" that you want to remain constant in the power triangle is the real power.
 
  • Like
Likes 1 person
  • #16
gneill said:
The power factor can be changed by adjusting the resistive or reactive parts of the load, or both. In "real world" practice the adjustment of power factor is usually done so as to maintain the real power to the load as a constant and reduce the reactive power (which produces no work and is thus wasteful for the generator to have to produce). The practical way to accomplish this is to place an additional purely reactive load in parallel with the original load in order to at least partially cancel out the reactance of the load. This brings the power factor closer to 1. So I suppose in this sense the "side" that you want to remain constant in the power triangle is the real power.

Thanks! that's what I was thinking too.
 
  • #17
Here's my take:
220 volts
22,000 watts
PF= .8

22,000/ .8 = 27,500 VA

Using pythagrean theroem I can find my VARS, or the vertical part of the triangle.
Vars= 16,500

I know that V^2/R= Power

In this case I'll substitute in VARS for power and 1/jwc for R.

V^2/(1/jwc)=VARS
V^2/VARS = jwc

220^2/16,500= j377C

Ignore the J, solve for C. (The J flipped into denominator will just make it minus 90 degrees which we already know)
C= 7.78 mF.

Sound right...or did I screw that up?

Two more things. Correcting to perfect power factor (unity or 1) creates harmful harmonics in factories...a .95 or .9 would be better in reality.
Also, the beauty of power factor correction is that it does NOT affect the voltage or current thru your motors or inductive loads.
If you had a motor with 220 volts and 125 amps at .8 power factor...It will still be 220 volts and 125amps at the motor WITH your power factor correction of 1. This is quite convenient since a motor will not run properly if you change the voltage or amperage!
 
Last edited:

Related to How to Calculate the Value of a Capacitor for Power Factor Correction

What is power factor correction?

Power factor correction is the process of correcting the power factor of an electrical system. Power factor is the ratio of real power (kW) to apparent power (kVA). A low power factor can lead to inefficiency and higher utility costs.

Why is power factor correction important?

Power factor correction is important because it improves the efficiency of an electrical system. A low power factor can result in wasted energy and higher utility costs. By improving the power factor, the system can use energy more efficiently and reduce costs.

How does power factor correction work?

Power factor correction is achieved by using capacitors to offset the reactive power in an electrical system. Capacitors act as a source of reactive power and help to balance out the reactive power from inductive loads, such as motors and transformers. This results in a higher power factor and improved system efficiency.

What are the benefits of power factor correction?

The benefits of power factor correction include improved energy efficiency, reduced utility costs, and increased system capacity. It also helps to reduce voltage drops and improve the voltage stability of the system.

When is power factor correction necessary?

Power factor correction is necessary when the power factor of an electrical system is below 0.95. This is typically the case in industrial and commercial settings where there are large inductive loads present. However, it can also be beneficial in residential settings to improve energy efficiency and reduce utility costs.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
9
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
6
Views
3K
  • Electrical Engineering
Replies
8
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
13
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
3K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
Replies
12
Views
2K
Back
Top