In summary: Hi all, I have a 90kva 3 phase 440volt/220volt stepdown transformer. When i test on no load ie secondary not connected to anything but the power is on, i get 220v between phases but to Earth or ground i get 1st phase 150volts, 2nd phase 104volts, and 3rd phase 150volts. Does this mean my transformer is U/S due to phase unbalance? Well if the secondary truly is not connected to anything at all then how can you expect any meaningful reading between a 'phase', and I think you mean 'leg', and ground? So tell us exactly what is hooked up.Sorry yes one leg and ground.
  • #1
spider2127
2
0
Hi all, I have a 90kva 3 phase 440volt/220volt stepdown transformer.
When i test on no load ie secondary not connected to anything but the power is on,
i get 220v between phases but to Earth or ground i get
1st phase 150volts
2nd phase 104volts
3rd phase 150volts
Does this mean my transformer is U/S due to phase unbalance
 
Engineering news on Phys.org
  • #2


Well if the secondary truly is not connected to anything at all then how can you expect any meaningful reading between a 'phase', and I think you mean 'leg', and ground? So tell us exactly what is hooked up.
 
  • #3


sorry yes one leg and ground. Ok i have a 3phase 440v/220v tranny that when connected to mulitple switchboards i get a reading of 155v red to ground,4v white to ground and 153v blue to ground. When i disconnect main switchboard and have nothing connected to the tranny my voltages from each leg to ground are as above
 
  • #4


i bet you're using a pretty good meter, maybe a DMM.

Try a real cheap analog one that's just a couple thousand ohms/volt.
sometimes low-tech works best.
 
  • #5


Does the transformer have a star point that you connected to ground? Otherwise, what Averagesupernova said applies. The voltages are floating, your measurements are meaningless. Don't throw the transformer away. :smile:
 
  • #6


when connected to mulitple switchboards i get a reading of 155v red to ground,4v white to ground and 153v blue to ground. When i disconnect main switchboard and have nothing connected to the tranny my voltages from each leg to ground are as above


Draw yourself an imaginary circle around the transformer, like a fence..
That fence represents the insulation of the transformer.

When you connect a voltmeter from one transformer phase to earth, you let a trickle of current flow out of transformer, through meter and over your fence into earth.

Apparently one of your switchboards connects white phase to earth.
So you get solid readings then, the meter current returns to transformer from earh via white phase.

But -How does that meter current get back into transformer when you've disconnected white phase from earth? How can it jump the fence?

It can't.
That's why you get flakey unbalanced readings, only a fraction of your meter current finds its way back over the fence. Insulation is imperfect and your meter is too sensitive.

Use a less sensitive meter and you'll read nearly zero on all three phases.

Or use a lightbulb instead of a meter.

it's a common problem ever since high impedance DMM's became so popular.
Typical DMM is 10 meg input.
Simpson 260 is i think 5Kohm/volt on AC, so on 250 volt scale = 1.25 meg.

A 1 kohm per volt el cheapo meter is what you need for that measurement.
Check the little yellow $ 9.95 GE analog meter at Walmart.


old jim
 
Last edited:
  • #7


Jim Hardy: Have you experienced the strange looks from people that I have when you tell them a low-tech cheap meter is still necessary?
 
  • #8


Averagesupernova said:
Jim Hardy: Have you experienced the strange looks from people that I have when you tell them a low-tech cheap meter is still necessary?

indeed.

I do 95% of my work with the $9.95 meter, even have an external resistor to make a 15 volt scale for automobile work. I soldered nice long test leads with alligator clips to it(nice Meuller copper ones) , because the cheapies are too short and fall out.

My high accuracy Fluke DMM is wonderful on rare occasions one needs precise resolution, maybe three times a year around the house.

When i retired the guys gave me a caricature drawn by the office wag portraying me in my old hat carrying a Simpson 260 and analog oscilloscope. With those two instruments you can fix anything.
 
  • #9


I have something similar to a 260 except it has a 3000 volt or higher range I believe. I don't have any test leads that fit it though. At least they didn't draw you with a pair of dry-cells taped around a door-bell.
-
Edit:
CORRECTION: It is a Triplett with a 6000 volt range.
 
Last edited:

Related to Hi all, I have a 90kva 3 phase 440volt/220volt stepdown

1. What is a 90kva 3 phase 440volt/220volt stepdown?

A 90kva 3 phase 440volt/220volt stepdown is an electrical device used to convert high voltage three-phase power (440 volts) into lower voltage single-phase power (220 volts).

2. How does a 90kva 3 phase 440volt/220volt stepdown work?

This stepdown uses transformers to reduce the voltage and convert the three-phase power into single-phase power. The transformers have multiple windings that are connected in a specific way to produce the desired output voltage.

3. What is the purpose of a 90kva 3 phase 440volt/220volt stepdown?

The main purpose of this stepdown is to provide a lower voltage single-phase power supply for devices that require 220 volts. It is commonly used in industrial settings where three-phase power is available, but single-phase power is required for specific equipment.

4. What is the difference between a 90kva 3 phase 440volt/220volt stepdown and a regular stepdown transformer?

The main difference is that a 90kva 3 phase 440volt/220volt stepdown is specifically designed to convert high voltage three-phase power into lower voltage single-phase power. Regular stepdown transformers may have different voltage and power ratings, and can also convert single-phase power into lower voltage single-phase power.

5. How do I choose the right 90kva 3 phase 440volt/220volt stepdown for my needs?

The right stepdown for your needs will depend on the power requirements of your equipment. It is important to consider the input and output voltage, power rating, and any other specifications that may be required. It is recommended to consult with a professional or an electrician to ensure you choose the correct stepdown for your specific needs.

Similar threads

Replies
5
Views
196
Replies
19
Views
2K
Replies
4
Views
8K
  • Electrical Engineering
Replies
1
Views
459
  • Electrical Engineering
Replies
12
Views
3K
  • Electrical Engineering
Replies
6
Views
2K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
6
Views
3K
  • Electrical Engineering
Replies
7
Views
4K
Replies
4
Views
4K
Back
Top