Calculating fuse size, current and voltage in a circuit

In summary: I have the same question, however it supplied the voltage at 120 and a load resistance of 20 OHMS. Also, it says to consider that the length of both, black and red hot conductor is 50 feet. I calculated 5.99910... which is 6 amps.In summary, we are given a circuit with a source voltage of 240V and a load resistance of 30 ohms. To calculate the size of the conductor and fuse, the current through the conductor, voltage across the existing load, and power consumed by the existing load under normal circuit condition, we can use Ohm's law (V=IR). The current is found to be 8 amps. Then
  • #1
Jon Canine
3
0
circuit.jpg


(a) Calculate the size of Conductor and Fuse, the amount of Current through the conductor, Voltage ACROSS the existing LOAD and power consumed by the EXISTING LOAD under normal circuit condition (when the switch of the above circuit will be closed).

(b) Calculate the overload current, voltage and power if additional two 30 OHMS loads are connected in parallel across the existing load. (When the switch will be closed).

(c) Calculate the short circuit current, voltage and power if the LOAD is shorted. (When the switch will be closed).

(d) What will happen to this circuit if HOT” CONDUCTOR COMES IN CONTACT WITH METAL RACEWAY OR OTHER METAL OBJECT.

(e) What will happen to this circuit under open circuit condition? Calculate the open circuit current, voltage and power if one 30 OHMS load IS connected across the existing load under this open circuit condition? (When the switch will not be closed).

Homework Equations



I = E/R

The Attempt at a Solution


[/B]
I know:

240 = 7.992 or 8amps.
24 + 0.001 + 0.001 + 0.001

How do i figure out fuse size and voltage?

i know this is very basic... Any help is greatly appreciated.
 
Physics news on Phys.org
  • #2
I don't see any fuse in the drawing. Do you understand what fuses DO? What do you need to know to know what "size" fuse you need?
 
  • #3
@phinds, I figure those blue capped rectangles are meant to be line fuses.

The problem statement is incomplete as it doesn't specify the source voltage or the load resistance. However, judging by the attempt at solution clues (I say clues because they aren't proper equations) I'm guessing that the source voltage is 240 V and the load resistance is 24 Ω.

We also don't know the length of the wiring, so determining the conductor size (assuming copper) from its given resistance is not possible. Of course, this may be some sort of Electrical Code test question where a normal residential circuit is assumed and wire gauge is determined by the load current.
 
Last edited:
  • #4
gneill said:
@phinds, I figure those blue capped rectangles are meant to be line fuses.
Yeah, I thought that might be the case but since the label said "conductor resistance" I took them to be resistors representing the conductor resistance.

The problem statement is incomplete as it doesn't specify the source voltage or the load resistance. However, judging by the attempt at solution clues (I say clues because they aren't proper equations) I'm guessing that the source voltage is 240 V and the load resistance is 24 Ω.

We also don't know the length of the wiring, so determining the conductor size (assuming copper) from its given resistance is not possible. Of course, this may be some sort of Electrical Code test question where a normal residential circuit is assumed and wire gauge is determined by the load current.
You're probably right ... I just have an antipathy to inadequate problem statements.
 
  • #5
damn... sorry. this part didn't paste:

Given that the VOLTAGE OF THE SOURCE =240V, LOAD RESISTANCE = 30 OHMS
 
  • #6
Jon, can you clarify the nature of the question? Is it an Electrical Code or Standards type question? Otherwise I don't see enough information to be able to determine a conductor size.
 
  • #7
Jon Canine said:
damn... sorry. this part didn't paste:

Given that the VOLTAGE OF THE SOURCE =240V, LOAD RESISTANCE = 30 OHMS
And you still have not answered the questions I asked you in post #2.
 
  • #8
This is just an electrical installations course. @phinds, you are correct - the fuses would be the blue rectangles by the switches. I understand what fuses do and I thought I needed: I (Amps) = P (Watts) ÷ V (Voltage) to figure it out...
 
  • #9
Jon Canine said:
This is just an electrical installations course. @phinds, you are correct - the fuses would be the blue rectangles by the switches. I understand what fuses do and I thought I needed: I (Amps) = P (Watts) ÷ V (Voltage) to figure it out...
Well, I suppose you could do it that way, but I don't see why you would want to do it the long way by computing power when you can just use ohms law directly
 
  • #10
Jon Canine said:
View attachment 78635

(a) Calculate the size of Conductor and Fuse, the amount of Current through the conductor, Voltage ACROSS the existing LOAD and power consumed by the EXISTING LOAD under normal circuit condition (when the switch of the above circuit will be closed).

(b) Calculate the overload current, voltage and power if additional two 30 OHMS loads are connected in parallel across the existing load. (When the switch will be closed).

(c) Calculate the short circuit current, voltage and power if the LOAD is shorted. (When the switch will be closed).

(d) What will happen to this circuit if HOT” CONDUCTOR COMES IN CONTACT WITH METAL RACEWAY OR OTHER METAL OBJECT.

(e) What will happen to this circuit under open circuit condition? Calculate the open circuit current, voltage and power if one 30 OHMS load IS connected across the existing load under this open circuit condition? (When the switch will not be closed).

Homework Equations



I = E/R

The Attempt at a Solution


[/B]
I know:

240 = 7.992 or 8amps.
24 + 0.001 + 0.001 + 0.001

How do i figure out fuse size and voltage?

i know this is very basic... Any help is greatly appreciated.

I have the same question, however it supplied the voltage at 120 and a load resistance of 20 OHMS. Also, it says to consider that the length of both, black and red hot conductor is 50 feet. I calculated 5.99910 amperes so 6 amps but not sure what to do next? Any ideas
 
  • #11
Mature student said:
Any ideas
Yes, start a new thread, with your own diagram.
 
  • #12
Has anyone figured this out? I have the same (a) (b) (c) (d) (e) questions above. my voltage is 120 , load resistance of 20ohms
Also, consider that the length of both, black and red hot conductor is 50 feet. I calculated 5.99910 amperes so 6 amps but not sure what to do next
 
  • #13
@Mature student & @basede92 -- Please start your own threads here in the homework forums with your question. Please be sure to fill out the Template with the Relevant Equations and show your work. Kind of strange that you both have such similar problems, but maybe the problem is from a distance-learning problem set or something.

This old thread is closed.
 

Related to Calculating fuse size, current and voltage in a circuit

1. How do I calculate the correct fuse size for a circuit?

To calculate the correct fuse size for a circuit, you will need to know the maximum current that the circuit can handle and the voltage of the circuit. Then, use the formula I = P/V, where I is the current, P is the power, and V is the voltage. This will give you the maximum current that the circuit can handle. Next, choose a fuse with a slightly higher rating than the calculated current.

2. What is the purpose of a fuse in a circuit?

A fuse is a safety device that is designed to protect the circuit from excessive current. It works by breaking the circuit when the current exceeds a certain level, thus preventing damage to the circuit and potential hazards such as fires.

3. How does voltage affect the choice of fuse size?

Voltage plays an important role in determining the correct fuse size for a circuit. The higher the voltage, the lower the resistance of the circuit, which means that more current will flow through the circuit. This means that a higher voltage circuit requires a larger fuse to handle the increased current.

4. Can a fuse be too big for a circuit?

Yes, a fuse can be too big for a circuit. A fuse that is too large will not provide proper protection for the circuit, as it will not break when the current exceeds a safe level. This can result in damage to the circuit or even a fire hazard. It is important to choose the correct fuse size for a circuit based on the maximum current that the circuit can handle.

5. What happens if I use a fuse with a lower rating than the calculated current?

If you use a fuse with a lower rating than the calculated current, it will blow or break when the current in the circuit exceeds the fuse's rating. This is an indication that the circuit is overloaded and the fuse is doing its job to protect the circuit. However, it is important to replace the fuse with one that is the correct size to avoid potential hazards and damage to the circuit.

Similar threads

  • Engineering and Comp Sci Homework Help
Replies
5
Views
979
  • Engineering and Comp Sci Homework Help
Replies
3
Views
906
  • Engineering and Comp Sci Homework Help
Replies
8
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
1
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
4
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
8
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
2
Views
1K
  • Engineering and Comp Sci Homework Help
Replies
0
Views
698
Back
Top